Hi all,

I im in the process of rewiring a kitchen and as Im taking the old cable out etc.. I come across a 20amp double pole switch.
Looking for some answer..

1. it was on the kitchen ring ?

2. It was feeding a single socket behind were the oven once was but it was in 6mm cable from the switch to the socket ?

Thanks
 
im in the process of rewiring a kitchen and as Im taking the old cable out etc.. I come across a 20amp double pole switch.
Looking for some answer
get a local spark in considering it will come under LBC.
 
  • Agree
Reactions: pc1966
Sounds like it was feeding an oven, not good practice!

But if it was a small oven (under 3kW) that came with a 13A plug then not an issue.

More commonly you see that for washing machines, fridge/freezer, etc, as an accessible means of isolation without pulling the thing out (which is often beyond a single person). It is not a requirement in the BS wiring reg, but in Scotland it is part of the building regs.
 
As pc said, sounds like it was feeding a cooker, but done badly.
Not really sure what your issue is though ? Surely if the kitchen is being rewired then all that crap will be stripped out and a new kitchen ring and cooker circuit will be installed properly ?
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
20amp switch on kitchen ring
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
3

Advert

Thread statistics

Created
Simba1,
Last reply from
Dazza1976,
Replies
3
Views
1,123

Advert