Hi, I am finishing up my design drawing for submission. I am working out all my circuit calculations and am a bit confused about what size I should use for my circuits which are supplies for my additional Distribution Boards ( Hotel, Pool, Summerhouse etc ). My hotel DB however even when accounted for diversity is still coming in as 136A. Is this excessive for a single circuit or does it not really matter?

I only worry because on my main DB ( The one C & G give you the Ze for ) I am getting a total demand of around 358A
 

Attachments

  • DB-1 Main Board.jpg
    184.5 KB · Views: 134
  • DB-1 Photoshop.jpg
    173.1 KB · Views: 131
Last edited:
My hotel DB however even when accounted for diversity is still coming in as 136A. Is this excessive for a single circuit or does it not really matter?

A single circuit could be hundreds or even thousands of amps of that is what the load requires.

In these design projects they are looking for you to do the calculations properly and come up with the answers, the scenarios they give you don't always reflect the real world.

136A seems pretty low demand for a whole hotel, but then what size hotel is it?
 
A single circuit could be hundreds or even thousands of amps of that is what the load requires.

In these design projects they are looking for you to do the calculations properly and come up with the answers, the scenarios they give you don't always reflect the real world.

136A seems pretty low demand for a whole hotel, but then what size hotel is it?
Yeah that was my thoughts to be honest was just wanting clarification thank you.

I have a total maximum demand of 340.96 but then did a calculation for diversity for the rooms themselves so like even though it's a 20A radial the real usage is only going to be like a laptop, phone charging, hairdryer etc only using like 9.24A

I have added additional DBs other than the hotel because I kind of looked at the project as a real-world situation and put separate Submains in the Kitchen and Pool area (also to help with the suggested maximum circuit size of 30m). I think this should be fine as I have worked out the theoretical Zdbs using R1+R2? Is this going to be okay?
 

Reply to 2365 Design Drawing Breaker Sizing in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

Hi I'm currently doing C&G 2365 Level 3 I'm working through the 305 design assignment (Swimming pool, hotel etc.) Other then this assignment I...
Replies
4
Views
4K
Hi everyone, I'm new here and was wondering if someone could help to get my college project calculations right. I'm about to start my 2nd year in...
Replies
12
Views
7K
Client currently has a DB in his outhouse. It feeds a pool pump and an air source heat pump. It is currently being supplied using a 4mm T&E cable...
Replies
9
Views
629
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Hi all, My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock