M

mk1tina

Hi Guys n Girls
Sorry if im having a dumb momment but I have a practical 2391 exam in march and i cannot remember for certain how to verify Vd.

Im assuming i can calculate the circuit length by taking the r1+r2 reading - then get the m'ohms per/m for both cables from the (OSG P166). Then divide the measured reading of say 0.3 by the milli ohms per metre to get the circuit length.

So do i then just do a simple Volt drop as per P124OSG using cable charts P274 in BS7671, my main concern is how about a 3phase Vd? You may not b surprised to hear i missed the Cable calc bit out the written exam... I passed it though lol :D

Just tell me what im missing, im not proud, after all I knew it all once and since forgot it all lol

Thanks
Mark the Spark
 
Last edited by a moderator:
you gont have tyo verify volt drop in the practical however i do recoment you study the periodic test sheets.

Hmmm. :) Ive been flicking throught the books and eventually things starting to come back online with the old brain!. I tried a few calcs and it all looks to be adding up at last..
As for the forms, thats this weekends browsing material LOL :D
I hear their wil be a motor circuit on the board, Im assuming u measure the IR between cpc and PN linked as the motor control will have a coil in it???

Thanks
Mark
 
they use the IET forms from the BRB and it will probbably be the periodic ones. pay attention to page 3 the tick sheets that is important.
 
You can always measure it :)

I didn't have to actually verify the volt drop in mine - the assessor

just asked me to describe how I'd do it.

I just said by measurement or by calculation (the way you described)

except you'ld need the circuit length to do the OSG calculations - could

be a bit tricky on a 2391 board because the circuits contain resistors.

Failing that, find the resistance of the cable, like you said (line and neutral)

and use ohms law with the design current.

Eg.

Lighting circuit:

R1 - 0.6 ohms

Rn - 0.5 ohms

Total - 1.1 ohms

Volt drop = 6 A x 1.1 ohms = 6.6 V

I think :D

R2
 
You can always measure it :)


Eg.

Lighting circuit:

R1 - 0.6 ohms

Rn - 0.5 ohms

Total - 1.1 ohms

Volt drop = 6 A x 1.1 ohms = 6.6 V

I think :D

R2


But that assumes a 6 amp load :)
 
volt drop is calculated using the desighn current not the rating of the overcurrent device. to truly calaculate it you have to have the true lenght of run, desighn current asw well as cable resistance which is why its frequently limited in a periodic
 
But that assumes a 6 amp load :)

Well I used 6A as an example of the design current - I did say:

. Failing that, find the resistance of the cable, like you said (line and neutral)

and use ohms law with the design current.:)


Like I said though, easiest way is to measure it.
 
you could measure it by taking incoming voltage at source then measuring voltage at end of line. it has to be under load though.


Thanks, Scotsparky, for reminding me of that fact:)

I was thinking you could just measure at the origin and then measure at

the end of the circuit - forgetting that the load counted.

In the 2391 this probably wouldn't be the simplest method then, as most

of the circuits don't have loads attached.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
2391 verfying volt drop
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
11

Advert

Thread statistics

Created
mk1tina,
Last reply from
mk1tina,
Replies
11
Views
4,689

Advert