wade88

Hi guys,

Looked over some previous posts and done some further reading, and attempted the calcs, just want to check that i am not miles off the ball park here with this. From what i have read harmonics and current down the neutral will cause massive fluctuations in results not to mention unbalanced phases but i would just like to get a broad figure so i have reference.

Cable run is 50 meters, 4 core SWA 25mm, clipped direct, 105 amps per phase.

Calculation i have been going on is:

mV/A/m x length x load / 1000 to find the approximate single phase volt drop in this circuit

and then multiply by 0.866 to take account for any current in the neutral

so im getting:

1.5 x 50 x 105/1000 = 7.875 x 0.866 = 6.81Volts.

Any one free to confirm they get similar results. Or have i missed an important part of the 3 phase calc process here.

Thanks guys


 
Or should it be 2.5 x 50 x 105/1000 x 0.866 = 11.36V

Cant decipher accurately what the mV is from the tables i have. Two tables are providing two different data sets but are titled the same? So not positive on which figure i should be using.
 
In the AEI cable table (I'm a poet and I know it) that I have to hand I have 25mm XLPE SWA as 1.65 mV/A/m...

Just to confuse you more...where are you getting your data from?...Im guessing it's XLPE your using?...
 
the figure i would use is from table 6E2, OSG. is 1.5mV/A/m.
 
Hi Wade88,
According to the IEE design guide the formula (mV/A/m)z x L x Ib /1000 should be used, ie, the z value of 1.5mV/A/m if the power factor of the load is not known. As above:smilewinkgrin:
 
the reason different volt drop figures for 2 & 3/4 core cables are given in the regs tables
is that it makes the adjustment for you.
follow Tels figures , youre making it too complex.
 
Just read your post...it should be single phase (2 core) volt drop times by square route of 3 divided by 2 (0.866) will give the 3 or 4 core volt drop in mV/A/m....
So it would be in your case single phase volt drop of 1.75 x 0.866 = 1.5mV/A/m
 
Last edited by a moderator:
lol oh thanks Tony....ill just jot that down on my lunch box for next time :ihih:

Yea 1.5 is what i had to begin with, so im happy with my results after that.

Thanks fellas.

I wish you all a great Christmas and a boozy new year.

Ben
 

Reply to 3 phase volt drop calcs in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

BIG place OK lots of electrical bits. but one on a 3 phase Radial is tripping its RCCB so i check the wiring making sure its tight and it has...
Replies
5
Views
336
I am trying to understand 3 phase volt drop. I understand single phase VD. Lets say we have a 70 meter run of 35mm, 5 core cable from the supply...
Replies
6
Views
2K
Hi! Once you've calculated the voltage drop in Volts - you divide by 400V for three phase right? For example: three phase 30kW appliance, 10mm...
Replies
5
Views
2K
Hello all, I signed up here for a little help. I bought a 3 phase bandsaw and went down the rabbit hole of VFD’s etc. ‘The motor is 3 phase 400v...
Replies
9
Views
1K
Hello, New trainee electrician so sorry if this is a dumb question I feel confident with calculating the volt drop for a ring and radial circuit...
Replies
2
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock