Just wanted to see if I'm being a bit too 'picky' but I've come across a few installations recently which have a 32A mcb for a radial circuit using only 2.5mm cable for which the current carrying capacity is approx 26A. I've been picking it up but it seems to be quite common. What do others do in these situations
 
AS chris has said 32amp for a ring 20 / 16 amp for a radial 2.5 is rated at 26 amps clipped direct so when protected by a 32 amp mcb its 6 amps more than carrying current capacity , and if its a rewireable fuse 3036 , even more as you have a correction factor of .725 to add to the equasion , and also if you have insulation covering it not exceeding 100 mm method 100 ,its rated at 21 amps more than 100mm its rated at 17 amps method 101 so max mcb rating would be 16 amps ,in my view your not being picky you are being correct so ,coding its a risk of overload so Code 1 it
 
Last edited by a moderator:
Cheers for the replies guys it confirms I was being correct its just that I've come across this so often recently it makes you wonder
 
yep alover the place especially in rewireable boards 3036 say 30 amp fuse 3036 / 0.725 = 41.37 amps

in the case of other factors that may be required : In / Ca x Cg x Ci x .725 = Amps

Correction factors :
Ca ambiant temperature
Cg Grouping
Ci surrounded by thermal insulation
0.725 correction factor for BS3036 rewireable fuses
 
Im not convinced its a code 1, as it doesnt present an immediate danger.

What about spurs?

Edit: Once again i didnt read the op properly. Been a looooooooong day. :D
 
It could if you stick large loads on it , understand what your saying about spurs but these normally are short lengths,however from the CDU it could be right through the loft and have more than one socket on it , when i do a PIR if i find these i test them indipendantly and some time you can have anything up to 10 sockets on it hence my reason for Code 1, jason i know how you feel get a beer and stick you feet up
 
Last edited by a moderator:
did a cu change the other day and found the immersion heater on a 30 amp rewirable with a 2.5mm cable. cable in conduit in a brick wall (equivalent derating of method B (if that is conduit on a wall) I believe, memory fades as the night wears on).

was tempted to put the new mcb in as a 32A.

the load (based on kw rating of immersion elements and other 'stuff' being fed from the circuit was around 20A.

good IR and very short run so low R1+R2 on the cable. about 15years old installation.

what would you guys have installed as a breaker?
 

Reply to 32A mcb on a 2.5mm cable in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Ok i may get slated for this one but here goes; A bit of background info first. Its been a while since ive looked at my iee regs, and ive not...
Replies
12
Views
2K
Hi, I have a book on domestic wiring which says that everywhere there is a change in current carrying capacity along a circuit there must be some...
Replies
3
Views
289
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
922
Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
678
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock