Hi all,
Doing a new build barn conversion installation and the lighting has been designed by a consultant. They've specified some 5A sockets for plug in lamps.. never done these before although I know the plugs and sockets are available.. round pin type.
Some of the arrangements are for 2 way switching so am I right in thinking the only way to do this is to treat the socket as basically the lamp and switch it locally using standard 2 way switches and intermediates adjacent to the sockets?
I'm planning to use dedicated 6A radial circuits using 1.5mm t&e does this sound ok?. There are a maximum of 6 outlets on each radial ..
Cheers..
 
You can put the switches where you want but three plating won't be practical as the sockets don't have loop in terminals so bring the live and neutral to the switches and connect that way.
 
Yes that's what I figured.. for bedside lamps there are also 2 way switches either bedside for the ceiling light too so I was going to put in 2 way 2 gang switches each side of the bed for 2 way switching of ceiling and bedside lamps..
 
Ok...., I do have plenty of ways in a 16 way con unit though so I thought it would give a bit of convenience to put all the 5A lighting skts on a separate mcb. I think there's 3 x 5A radials, 2 upstairs and 1 downstairs so these could go in one or maybe 2 mcbs.
 
about 5 years. Yes I agree it would be easiest and cheapest option to have them all on lighting circuit. just thought as I have the spare ways at dB it would bnice to segregate them. it's quite a large and complex lighting circuit as it is with sensor ensuite lights and extra wall lights everywhere etc. thanks for all helpful replies..
 
about 5 years. Yes I agree it would be easiest and cheapest option to have them all on lighting circuit. just thought as I have the spare ways at dB it would bnice to segregate them. it's quite a large and complex lighting circuit as it is with sensor ensuite lights and extra wall lights everywhere etc. thanks for all helpful replies..

Wouldn't it be better to split the one large lighting circuit into two smaller ones?
 

Reply to 5A lighting sockets circuit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
284
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
728
Hi. I'm in the process of getting my qualifications and am taking on some small jobs for family to try and get some experience in. Today I was...
Replies
17
Views
837
I'm looking at a vending hot drinks machine 2.9kW that has a thermostatically controlled hot water tank permanently attached to a water supply...
Replies
2
Views
232
Hi guys I have some industrial lighting circuits to wire in a workshop and was after some fresh ideas/suggestions as to how i could best do this...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock