Howdy All,

just after a 2nd opinion as i'm doubting myself.
I went to a property to look at replacing the ccu, I noticed what I thought was a 6mm cooker circuit on 32a
But found it was feeding another ccu in the kitchen (Extension)
I couldn't open the ccu as it was boxed very tightly!!
it has 4 circuits feeding the kitchen and rooms above. Bedroom/bathroom
cooker 32a (hob 5.5Kw & oven - unsure of Kw)
sockets 32a
radial 16a (unsure)
Lights 6a

I recommended upgrading the cable to 10mm and on 45a due to the loads
The cable is run above the ceiling
They don't wanna replace as its "working fine and always has been"!!

I just want others views.
appreciate any reply's
 
IMO it's pure luck that this sub circuit (32A) has not gone pop feeding 4 circuits some of which are of substantial size, any cable feeding between to cu's is not a sub main, it's a sub circuit just like any other circuit fed of a CU. Technically the circuit is sized correctly to the cable. Terrible circuit design and undersized for what it's supplying. A genuine sub main would be better. Out of interest what protective devices are there in both CU's.?
 
IMO it's pure luck that this sub circuit (32A) has not gone pop feeding 4 circuits some of which are of substantial size, any cable feeding between to cu's is not a sub main, it's a sub circuit just like any other circuit fed of a CU. Technically the circuit is sized correctly to the cable. Terrible circuit design and undersized for what it's supplying. A genuine sub main would be better. Out of interest what protective devices are there in both CU's.?
Cheers for your reply, the protective devices in each CU are 3871, was looking at changing the CU's to add RCD protection.
 
Seems likely that the OCPD could well be running over its rated current quite often.
It probably comes down to if they use plug-in heaters or not.

The 32A upstairs rooms' sockets probably draw an amp or two normally otherwise. Cooker can be above 32A of course but not normally for long periods. The 16A radial is more of a worry as it might be immersion heater so a real long-term draw. Lights largely can be ignored.

But I agree with the above, a proper sub-main in SWA fed from fused-switch would be better design. But why, why, WHY? Surely the house should have been wired from the normal CU for everything unless it is truly massive!
 
It probably comes down to if they use plug-in heaters or not.

The 32A upstairs rooms' sockets probably draw an amp or two normally otherwise. Cooker can be above 32A of course but not normally for long periods. The 16A radial is more of a worry as it might be immersion heater so a real long-term draw. Lights largely can be ignored.

But I agree with the above, a proper sub-main in SWA fed from fused-switch would be better design. But why, why, WHY? Surely the house should have been wired from the normal CU for everything unless it is truly massive!
There’s no electric heaters, I couldn’t verify but I think the 16a radial could be an oven or boiler.

As for the sockets it’s not just the upstairs sockets it’s also the kitchen sockets.

I’m guessing when they put the extension on they they decided to use the old cooker cable, then new circuits from there.
 
IMO it's pure luck that this sub circuit (32A) has not gone pop feeding 4 circuits some of which are of substantial size

It's not luck, it's diversity.
, any cable feeding between to cu's is not a sub main, it's a sub circuit just like any other circuit fed of a CU.

Neither submain nor subcircuit are correct terminology. Circuits are either distribution circuits or final circuits.
 
It's nothing to do with being a newcomer, it's keeping up with changes in terminology and regulations etc.
Does it really matter if old terminology is being used, the OP and other members knew exactly what I was saying.
You are a guy with great knowledge but I feel sometimes you try and bait an argument for arguments sake, shame really.
 
Does it really matter if old terminology is being used, the OP and other members knew exactly what I was saying.

I'd say yes it does matter and I don't really follow what you were saying either.

It appears to me that you were trying to say that the circuit is not a submain (distribution circuit) when it quite obviously is.
 
Bit of head scratching here as I wouldn't have consider this a sub-main, but I guess it is as it's fed from the 'main' distribution board.

What would you consider it to be?

Bearing in mind the options are distribution circuit or final circuit, and it is clearly not a final circuit.

This is a pretty binary decision, it is either one or the other.
 

Reply to 6mm kitchen sub-main in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello everyone, I'd like to seek your input on a matter. I'm in the process of designing the electrical connections for the following kitchen...
Replies
38
Views
3K
Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K
I have just had my kitchen redone and the kitchen rewired with a new 6mm cable installed for an electric cooker. However I have changed my mind...
Replies
10
Views
2K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
682

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock