that's fine, platty, until the insulation muppets arrive and reduce your ccc to 27A.

First post says NO INSULATION so i was just answering the original question and stated that 6mm is ok for REf C

If REF method 101 then 16mm cable is just big enough but i would not like to wrestle it into a pull switch !!
 
i totally agree with you. we design a circuit to comply under existing conditions. if these itchysnot installers don't know any better than to smother cables, then they should get fresh employment selling the big issue.
 
i totally agree with you. we design a circuit to comply under existing conditions. if these itchysnot installers don't know any better than to smother cables, then they should get fresh employment selling the big issue.

Tel, the insulation installers is monkey see monkey do they don't know about all the Calcs to do with cables etc they just fill the area with the stuff off the van and move on to the next job.
its us poor guys who have to think of all that derating factors etc
 
Just or all the posts about insulation (itchy Snot, I think some of you call them). You can't future proof for every eventuallity. If you did, then you may as well put cabling in from the roof just in case customer wants PV later on.
 
Just or all the posts about insulation (itchy Snot, I think some of you call them). You can't future proof for every eventuallity. If you did, then you may as well put cabling in from the roof just in case customer wants PV later on.

Totally agree mate. If the loft has only 4" of insulation tho, it is very likely that at some point in the foreseeable future there will be some addition. I always take my oval conduit 6 inches above existing insulation for just such an eventuality :)
 
Totally agree mate. If the loft has only 4" of insulation tho, it is very likely that at some point in the foreseeable future there will be some addition. I always take my oval conduit 6 inches above existing insulation for just such an eventuality :)

Good thinkin' bonny lad .. are ye a Geordie by any chance?? ....... If yer not, divven't worry ... aahl make ye an honourary one for noo.
 
Havnt bothered to read the other pages so this may have been said. 6mm will do for a while, id never put a 6mm cable in for anythin over 8.5kw shower, simply because ive been to far too many homes where a 9.5kw has been on an 6mm and the cable is burnt out/switch etc. Over a period of time, the 6mm will begin to melt, usually from the women who spend an eternity in the shower ! 10mm everytime for showers over 8.5kw every time.
 
Tel, the insulation installers is monkey see monkey do they don't know about all the Calcs to do with cables etc they just fill the area with the stuff off the van and move on to the next job.
its us poor guys who have to think of all that derating factors etc

I think that we must recommend that all new circuits installed in lofts that have no loft insulation, should be installed, at least 300mm above the plasterboard, on the loft wall or along appropriate battens installed for the purpose.

This would circumvent the "monkeys".
 

Reply to 9.5 kw shower on 6mm ? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Hi, Same project as detailed in my other post (I want to run shower cables to the CU whilst the kitchen ceiling is disturbed). I'm going to...
Replies
5
Views
3K
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
213
Hi all, Have a relatively simple question. Doing a rewire to make a circuit in a single room. My father is a retired spark, so no worries about a...
Replies
7
Views
2K
I have a TPN board that will feed 8-10 sub boards. The loads on each board are negligible 5-10 amps peak but mostly 1-2 amps. The distribution...
Replies
26
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock