I have just tested an 185 4 core SWA, and have got readings of 40 Megs on L2 to earth and L3 to earth. Although this is accepatable according to the regs, I feel it is unacceptable as a NEW installation, and indeed there is evidence of water on some of the switchgear, which clearly indicates water tracking between the cores. So I am refusing to pass it untill readings of >200 Meg are acheived. This equipment actually forms part of the EDF supply cable, so is in effect theirs, so I suppose its up to them to accept it.

Would like to have peoples thoughts on this?

whether to pass it or not? will EDF accept it?

Thanks
 
For a newly installed SWA that's carp, I'd not except it all, but that's me I like it to be perfect.
 
40 million amps have to flow or something like that to create a short. But as you say if it's new it should be higher, mYbe will dry out.
 
I tested this cable last week, and did indeed advice to put some space heaters next to the switchgear.
 
Come on get a grip before the thread gets trashed.185mm2 cable and water between the cores? Pull yourself together man.
 
Fire it up an test in a week. Might start to rust if wet
 
You cant fail it... Its 40x greater than the minimum requirement BS7671.. It could be seen as fraud leading a customer into thinking its not passable!
 
How do you explain the readings? what's the environment, humidity, type of termination enclosures, what sort of spark did the glanding etc

How can anyone make a judgement on a forum?
 
You cant fail it... Its 40x greater than the minimum requirement BS7671.. It could be seen as fraud leading a customer into thinking its not passable!

This job has 3 risers, each with an 185mm 4 core feeding it. EDF turned up on Frfiday and QA'd the other 2 supplies and equipment. Unfortuately I was not part of the team when EDF were on site. So must be something in it.
 
How do you explain the readings? what's the environment, humidity, type of termination enclosures, what sort of spark did the glanding etc

How can anyone make a judgement on a forum?

The enviroment is the same as the other 2 185's that were tested and were fine, with readings >499 Meg tested at 1000V

- - - Updated - - -

Is there a nest of insects at the terminations

lol .......No
 
You cant fail it... Its 40x greater than the minimum requirement BS7671.. It could be seen as fraud leading a customer into thinking its not passable!
If this cable is part of the DNO supply then it is not subject to BS7671, it will be whatever the DNO decides is acceptable (EDF in this case).

If this is a lot lower than other identical cables/risers then I would be concerned too, did you try wiping the terminations riser etc. with a dry clean rag ? it is more likely the terminations or the switchgear being damp than between cores, and did you test between all of the cores (all 10 tests) ?
 
If its part of the DNO then why are you ir testing this cable?
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Acceptable readings for a NEW installation
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
28

Advert

Thread statistics

Created
Guest 004,
Last reply from
spark 68,
Replies
28
Views
3,955

Advert