Ok. I am a catching up slowlyIf the PFC was 2090A, then you would use the manufacturers data and realise that the tripping time would then be closer to 0.001s.
The higher the PFC, the faster the breaker will trip. That is the slight flaw in your logic![]()

The only trouble I have with that is the data I have just looked at (MK sentry) stops at 0.01s. I do see that the time would be less than that but I am not convinced I could reliable guess how much lower as it will be limited mechanically (just thinking that a lot of RCDs I test go at around 0.01s regardless of current). Plus the graph for MK definitely shows the curve tending to horizontal below 0.1s. Doing to sums in reverse and using the cable size from the "appendix 3" results (0.87mm2) then the real trip time at 2090A would have to be 0.0023s. Feasible but I'm still (edit) not convinced.
The thing is (and I know you guys are going to disagree with me) I think this is a misuse of the tables in appendix 3. I believe these tables are giving the minimum current required to achieve a certain trip time. i.e they are to calculate the max Zs. I don't believe they hold up in this case where you are effectively assuming the breaker will limit the current to 320A for 0.1. I know you guys don't believe this is actually what happens but it is what would have to happen for the adiabatic results to make any sort of sense.