Actually not sure if that was clear - I'm new to crossover switches so I'll explain it better.

I disconnected one wire from crossover switch and a helper switched the lights on/off with the 1st or 3rd switch. When 'off' the lights didn't glow, I put it down to the 'off' circuit being broken at the crossover wire I pulled.

I then put a DMM on the pulled wire and measure 60-70mA and 2-3mA whilst helper used the other switch.

With the ammeter connected the LEDs did glow when off - ie the current was being drawn through the crossover switch.

I'm not really familiar with AC either so if that terminology is wrong assume I'm in thinking in DC:)
 
Hi - you've tried your best, but IMHO you should make friends with a real Electrician now. Us virtual ones can't be there to keep you safe doing what you're doing.
 
  • Like
Reactions: DPG and w0z
Thanks, but I'd like to understand what I've found out so far... I think with the suggestions above I've disproved miswiring in the ceiling (ie anything after the crossover switch), and with a 3mA current when 'off' I think it's proved to be either miswiring before the crossover or capacative coupling - so it comes down to whether 3mA is a reasonable figure for CC?
If it is then I can go down the 'try a different LED' route before I get an electrician?
(I actually spoke to 2 acquaintances who are electricians and they both looked at me as though I was mad - "voltage cannot be 40V when 'off'"! - so I'd prefer to find someone who has seen this before)
 
I agree with Wilko

In the famous words of Dragons' Den "I'm out" but I will extend you the courtesy of telling you why.
This is one of the most confusing threads I've read on here and begins with many incorrect assumptions and much missing information, but the dealbreaker for me is that I don't feel that you understand what you're doing and that you don't really understand electricity at all. That makes you a danger to yourself and others. I'm sorry if that sounds harsh.

Crossover switch? Do you mean intermediate switch? (where was that in the original post?)
Who connected the lights?
Did they ever work properly in the first place?
Did you draw a diagram of your wiring?
Could you (draw a diagram)?
Would you know if the lights were ever working correctly? (it's not obvious with some leds).

My guess is some of the lights are or have been incorrectly wired in series with each other when off, in some way, perhaps dangerously which is why you're measuring 40v, but frankly I don't trust any of your measurements anyway.

By the way 14 x 5w leds = 70W (estimate as leds inexact) Halogen? 10W? 20W?
I'll leave you to work out the theoretical current (with pen and paper please, not with a screwdriver and DMM). Clue- it's more than 70mA
 
  • Like
Reactions: DPG
I agree with Wilko

In the famous words of Dragons' Den "I'm out" but I will extend you the courtesy of telling you why.
This is one of the most confusing threads I've read on here...

Crossover switch? Do you mean intermediate switch? (where was that in the original post?)
Who connected the lights?
Did they ever work properly in the first place?
Did you draw a diagram of your wiring?
Could you (draw a diagram)?
Would you know if the lights were ever working correctly? (it's not obvious with some leds).

My guess is some of the lights are or have been incorrectly wired in series with each other when off, in some way, perhaps dangerously which is why you're measuring 40v, but frankly I don't trust any of your measurements anyway.

By the way 14 x 5w leds = 70W (estimate as leds inexact) Halogen? 10W? 20W?
I'll leave you to work out the theoretical current (with pen and paper please, not with a screwdriver and DMM). Clue- it's more than 70mA

Thanks for telling me why - but if you would bear with me I think I can clear up a lot of your points...

The crossover/intermediate switch was assumed because there are 3 switches so there has to be one, right? When asked to disconnect a switch I picked the middle one.

The original CFL lights did work fine.

I put up the new lights - one-for-one replacements, I don't see how I could have miswired them.

The 'off' voltage is definitely there, measured with DMM and analog meters.

I do understand electricity and I put the 63mA as the observed measurement rather than calculate it. The AC calculation is different from DC and, I admit, 'power factor' means little.

However I'm happy with the 63mA because -as you say - LEDs are inexact and I'm happy to assume my DMM is not calibrated... I see the important thing as proof the current is being drawn through the crossover switch, and if I disconnect that then the LEDs go off - proving no other source of current after the switch.

Don't worry if you want to stay dropped out, I'm not getting bolshy about it, I know how these things can be difficult over a forum... however I got such useful replies at the beginning I just wanted to follow up on them in the hope of a diagnosis.

In short, am I right in thinking it's still induction/CC? Can that generate 3mA ? Or is there a way to calculate CC from the length of live wire going back and forth over the 3 switches?
 
Several people above have answered your question about the stray voltage being capacitive /inductive pickup across adjacent cables. Very unlikely to illuminate a halogen lamp.

Needs a sparky in to do some thorough testing.
 
Capacitive coupling is normally enough to cause an occasional flash from LED or CFL lamps as the capacitors in the drivers very slowly charge and discharge.
For a halogen lamp to glow when switched off I’m pretty confident in saying something other than capacitive coupling is not responsible for this.
Capacitive coupling occurs in conductors which are floating (not connected to a source of power or neutral/earth. The halogen lamp is effectively a simple piece of wire which shorts the switched live to neutral and so negates any capacitively coupled voltage when switched off.
For the lamp to glow the switched live must still be connected to a source of power, and since it is only glowing and not at full brightness I’d say that connection has some appreciable resistance to it.

My guess would be a faulty switch or a joint box with something in it that shouldn’t be there, water or a mouse etc.
 
  • Like
Reactions: DPG
I agree with the above about getting an electrician to look at it.

If it is induction then it’s likely you can connect a contactor above the ceiling light somewhere and have the switches operate that. The contactor will disconnect live and neutral from the supply when not in use.

I think even in industry in control panels with hundreds of wires grouped together with tens of motor drives close by, I’ve never seen induction as high as 40 volts!
 
Thanks for telling me why .....

In short, am I right in thinking it's still induction/CC?
I doubt it.
Please read the answers you've been given so far.
 
  • Like
Reactions: DPG
I agree with the above about getting an electrician to look at it.

If it is induction then it’s likely you can connect a contactor above the ceiling light somewhere and have the switches operate that. The contactor will disconnect live and neutral from the supply when not in use.

I think even in industry in control panels with hundreds of wires grouped together with tens of motor drives close by, I’ve never seen induction as high as 40 volts!
OP' has now been told 3 times that it's very unlikely (read not) induced.
 
  • Like
Reactions: DPG
I think even in industry in control panels with hundreds of wires grouped together with tens of motor drives close by, I’ve never seen induction as high as 40 volts!

Im pretty sure you will have seen induction at much higher voltages than that considering induction is the basis of how generators, transformers and motors operate
 
Im pretty sure you will have seen induction at much higher voltages than that considering induction is the basis of how generators, transformers and motors operate

Yes of course, like the 15kva transformer I was working on yesterday.
But we were talking about unwanted induction between circuits in a residence.
 
  • Like
Reactions: DPG
OK, thanks for all of your help.

I understand that the glowing halogen has killed the induction theory, which is a shame because I felt that was probably curable.

Ironically I did change some LED bulb brands and when they didn't glow I thought it was solved, but on removing the halogen they did glow.

I agree it now requires proper testing of the circuit which I'm happy to delegate.

I'm still curious though about the theory of what is happening - if the rogue current is only there when the RCD is closed, the live wire is the only possible source... correct?

So if there is a fault with the live wire, and if it is before the switches, the fault won't be detectable - ie the switches will still cut out the rogue current.

And yet if there is a fault after the switches then the LEDs would have glowed even after I disconnected the crossover switch - but they only glowed when I closed the circuit with the ammeter (and saw the 3mA).

Apologies if my question is too 'DC'-like :)
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Advice on LED inductive voltage preventing LEDs switching off
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
32

Advert

Thread statistics

Created
Stagbeetle,
Last reply from
Stagbeetle,
Replies
32
Views
9,945

Advert