The maximum tabulated value for a protective device is 1.85 ohms.
And the measured R1 + R2 is 1.03 ohms
What would the maximum ze 've expected to be allowed.
A) 0.35
B) 0.82
C) 21
D) 0.21
For some reason I typed in
1.03 x 0.8 on the calculator as I had the rule of thumb figure in my head and it came out a 0.82
So I want with that and that's what the answer was
Does that mean I applied the right maths
Or did I just get coincidentally lucky?
A) 0.35
B) 0.82
C) 21
D) 0.21
No.
Yes.
The formula for calculating Ze is:
Ze=Zs-R1+R2
Ze=1.85-1.03= 0.82 ohms
Yes the Zs is normally measured when the cables are at room temperature of around 20 degrees.
The Max Zs permitted is for when the conductors are at maximum operating temperature which for PVC is 70 degrees, at which temperature the resistance will be higher. So the measured Zs is multiplied by the 0.8 factor to account for this difference.
Reply to Another question in the UK Electrical Forum area at ElectriciansForums.net
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Hi there, I'm Currently doing my design calcs for my college project and doing the actual Zs calculation. Formula is Zs= Ze (or Zdb) + (R1+R2)...
Hi everyone, I'm new here and was wondering if someone could help to get my college project calculations right. I'm about to start my 2nd year in...
7K
Hi, and thank you to anyone who's taking the time to read my question. i'm struggling with the outcome of an adiabatic equation i'm doing and...
My brain has been exercised a bit by this. Am I on the right lines with this extremely simplified example: If we take: -TNCS installation with a...
4K