So I got a call from a customer asking me about something I did in Feb 16 - so I duely paid a visit. Knowing they had had some work done I asked if I could see the certificate..... as I didn't take mine with me!
Now bearing in mind a new fuseboard had been fitted, the kitchen had been hacked around, downlights had been fitted and a wall removed I was expecting an detailed EIC........
Er no, the EIC simply said replacement fuseboard..... which had all 10 "slots" used.
This is a photo of the test results sheet.........
Sorry its side ways
Anybody want to play "spot the mistake / ommision / unusual entry" with me?
Ring final 9 appears to be rather long and open circuit on the lines. Seems they didn't loop it either or several of the others.
They also have 4.0 cpcs on the 6.0 cables, assuming T&E.
No IR readings.
Dear me, I could have fabricated a better test sheet sitting at home with a cuppa!
Not supposed to put LIM on an EIC.
There's and old saying "If it looks right, then it is right"
This clearly isn't right.
It's not just you ... I'd be suggesting to Client the last lot should return and provide one done to standard. If they hesitate, perhaps offer to email original to their CPS for review :rolleyes:
How can they tick polarity on the circuits they haven’t tested or entered results for R1+R2 or Max ZS reading? Ring Circuit 9 20000 so near enough useless continuity on R1, the list of errors and inconsistency just keeps getting worse. So what was the IPf at that board left blank too.
How is it applicable?
To start with, the form asks for the maximum allowed by BS7671.
I guess technically none of it is applicable as the certificate is for a board change.
I wonder why it’s applicable for one RCD, but not for the other two?
It’s also odd that they conducted no IR tests.
I was wondering about forwarding a copy to Elecsa .. I do have his details and number!
Maybe get the customer to get in touch with elecsa and send a copy of that cert complete with installer name and number and ask them to confirm if that certificate is genuine.
I think he means you don’t measure a zs for the rcd hence the box is marked N/A on the certificate for both.
Also why would you write 1667 ohms for a 30mA rcd for maximum zs when that referes to the touch voltages not rising above 50 volts it’s not really applicable to the certificate in my opinion, at least that is I’ve never wrote it in unless the rcd is proving fault protection as the sole means such as a TT system.
Reply to Are you based in Frimley???????? in the UK Electrical Forum area at ElectriciansForums.net
I have been asked to rewire an antique metal standard lamp. It has been rewired previously, but not earthed..! One of the screws on the base has a...
5K
Hi all -- full disclosure I am a 'DIY-er' but wanted to post here for greater visibility seeing as I certainly won't be doing this work myself...
4K
Recently visited a new build to do a very minor job and spotted a few dodgy looking items so Client asked me to do an EICR. Following items I...
I hope this is the right place to post this, please redirect me if not. I've spent quite some time reading the forums, so I apologize if I've...