Discuss BS3871 on EICR classifiaction code? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
22
I have searched for an answer to this question but to no prevail.

BS3871's.... should these be changed? I have just done an EICR on a board with these and no RCD for lights serving bathroom but it has an RCD protecting all sockets, shower and the cooker circuit... now I have given 2 x C2 codes because 1 the RCD doesn't trip in the allowed time and 2 for no RCD protection or supplementary bonding etc for the lights in bathroom

BUT hypothetically... if it was all protected by a fully working RCD would I be ok in saying BS3871's are ok still? Or does it need to comply with regards to disconnection times? If so where do I find these disconnection times?

Thanks in advance
 
I have searched for an answer to this question but to no prevail.

BS3871's.... should these be changed? I have just done an EICR on a board with these and no RCD for lights serving bathroom but it has an RCD protecting all sockets, shower and the cooker circuit... now I have given 2 x C2 codes because 1 the RCD doesn't trip in the allowed time and 2 for no RCD protection or supplementary bonding etc for the lights in bathroom

BUT hypothetically... if it was all protected by a fully working RCD would I be ok in saying BS3871's are ok still? Or does it need to comply with regards to disconnection times? If so where do I find these disconnection times?

Thanks in advance
I believe BS3871s are still considered compliant. You'll find max Zs and other info for these in the current on site guide.
 
Surely if the lighting in the Bathroom is above 2.25m no RCD protection, CPC in place, its no code?
True, but irrelevant. If no RCD was required when it was installed, then it's a C3.
You test to the current regs. Anything that doesn't meet the current regs, but met the regs. in force when it was installed is a C3*. Anything that doesn't meet the current regs, and didn't meet the regs in force when it was installed is a C2.

* I'm referring to 'modern' wiring, not stuff installed pre '50's, so please don't bring up fused neutrals.
 
So are you saying if it’s above 2.25M in bathroom and has no RCD protection and no supplementary bonding that is a no code?

obviously C3 for no RCD on lighting in general, but the bathroom requirement I would have put at C2.

this is a question not a disagreement.
 

Reply to BS3871 on EICR classifiaction code? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

So I know why it is done, where it is done and how it’s done, but I’m yet to see a scenario where there is shock danger in a typical bathroom in a...
Replies
32
Views
1K
I have an new set of circs here... Landlord in Cyprus EICR needed in empty flat. No credit on meter. Need power for Ze (TNCS) and RCD test at...
Replies
11
Views
467
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
763
Good Afternoon All Currently doing an EICR on common parts of a big site with multiple blocks. All blocks have outside garden spike lighting in...
Replies
11
Views
591
Another thread asked about two circuits sharing a common multi-core cable and regulation 521.8.1 was mentioned. A friend of mine has inherited...
Replies
13
Views
691

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock