It seems its a C3 = Improvement recommended, as it does not conform to the latest regulations (which are deemed to be an improvement), but not a C2 or C1 as it does not present a hazard.
That would be 701.415.2, and 411.3.2.2, 701.411.3.3, 411.3.1.2, if this was a downlighter only accessible with a tool, how would you code that then?
I suppose in truth the sensible thing to do is to protect anything in a shower or bathroom with an RCD which in essence everything in a modern two RCD board is.
The location of the luminaire is not relevant it serves a location containing a bath or a shower, zones in this case are irrelevant.
IMO the location of the luminaire is relevant in some cases, from a coding point of view rather than compliance. If it could only be reached by climbing a ladder, then a C3 for no RCD and no supp bonding. If within reach, then C2 for the same
It is serving the location so whether a tool is required or not is neither here nor there.
True, but irrelevant. If no RCD was required when it was installed, then it's a C3.
You test to the current regs. Anything that doesn't meet the current regs, but met the regs. in force when it was installed is a C3*. Anything that doesn't meet the current regs, and didn't meet the regs in force when it was installed is a C2.
* I'm referring to 'modern' wiring, not stuff installed pre '50's, so please don't bring up fused neutrals.
Not really. A socket installed to an earlier edition which could reasonably be used to power equipment outside would be a C2 if no RCD protection.
I think you meant 'you inspect to the current regs' testing hasn't changed over the years (part for maybe AFDD's). ???
C2
Absence of supplementary bonding where
required, such as in a location containing a
bath or shower, where any of the following
three conditions are not satisfied:
❍ All final circuits of the location comply with
the requirements of Regulation 411.3.2 for
automatic disconnection, and
❍ All final circuits of the location have
additional protection by means of a 30 mA
RCD, and
❍ All extraneous-conductive-parts of the
location are effectively connected to the
protective equipotential bonding (main
earthing terminal).
So just because it was compliant 50 years ago doesn't mean it isn't a C2 on an 18th edition EICR
The latest best practise guide suggest that :
for class 2 fittings
Absence of supplementary bonding for installed Class II equipment where required (such as in a location containing a bath or shower), in case the equipment is replaced with Class I equipment in the future
this does not require reporting or any code
Reply to BS3871 on EICR classifiaction code? in the UK Electrical Forum area at ElectriciansForums.net
So I know why it is done, where it is done and how it’s done, but I’m yet to see a scenario where there is shock danger in a typical bathroom in a...
I have an new set of circs here... Landlord in Cyprus EICR needed in empty flat. No credit on meter. Need power for Ze (TNCS) and RCD test at...
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Good Afternoon All Currently doing an EICR on common parts of a big site with multiple blocks. All blocks have outside garden spike lighting in...
Another thread asked about two circuits sharing a common multi-core cable and regulation 521.8.1 was mentioned. A friend of mine has inherited...