Apologies for the delay in replying. Ive been stuck on a brutal night shift for the last week so its been a bit of eat sleep and work...repeat. Plus i didnt receive any notifications for replys...

Anyway, huge thanks to everyone for chipping in and although im fairly confident ill pass, i just find these foibles (love that word) annoying.
 
  • Like
Reactions: timhoward
If you read the list in the regulation you mentioned, the key thing is that in all cases you can't possibly have both supplies on at once. A separate switch for each doesn't prevent you turning them both on. The point of the regulation is that you mustn't ever be able to do that.

Ooops. ive just reread the question and realised my mistake! Should pay more attention.
 
  • Like
Reactions: DPG
I don't have a copy of the questions, etc, but this is one odd aspect where common usage of 'live' differs from the definitions.

Live = Any current-carrying conductor under normal use (so all but the CPC)
Neutral = A live conductors that somewhere is connected/referenced to Earth.
Line = The live conductor(s) not referenced to Earth

Indeed it really is the referencing of a current-carrying conductor to Earth that defines neutral, and how/where that is done is of course on of the key aspects of the supply.

While an IT supply may not have any reference to Earth, most of any significant power level (e.g. excluding shaver supplies) do by some high impedance so they technically can have a neutral even though a single line-Earth fault has no immediate impact on operations as normally the earthing impedance is quite high and designed to sustain such a single fault. Used for situations where you really don't want an immediate interruption if at all possible (e.g. operating theatre supply, ship electrics, etc) and it is under skilled supervision.

Thanks for the detailed answer. I appreciate the effort as not being an electrician, it all adds to my knowledge. Again, ive just reread the question and i think ive made the same mistake of trying to be too quick in doing my answers. Deep breath needed when i get round to doing the exam for real.
 
  • Like
Reactions: DPG and pc1966
yay 86% !!!!! Well chuffed with that.

geddin. Now i need to find a friendly local electrician to 'train' with before i do the T&I course.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Suffolk
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician
Business Name
Marine electronics

Thread Information

Title
BS7671 Help with some PFE questions
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
23

Thread Tags

Advert

Thread statistics

Created
clanky,
Last reply from
clanky,
Replies
23
Views
3,950

Advert