This is old Haes panel, installed in a council special needs learning centre, and maintained by a blue chip all building maintenance company. For the past 3 years they have serviced it every quarter, and given it a full bill of health certification.
On working on a building extension, we checked the existing system, only to find numerous faults.
The batteries were dead & dry, the bell circuits were disconnected, and rewired on a unmonitored relay as in photo, using 4 core cable. The system had random smoke detectors in classrooms, but non in corridor areas, meeting no category what so ever.

Conclusion we refused to connect into the existing panel, and fitted a temporary panel until advised.
Council engineers agree we our findings and request complete new system to meet L1. Investigation and questions now being ask, how was this passed on 3 years of maintenance...? Are theses companies upto the job..?

2015-04-25 09.02.55.jpg2015-04-25 09.03.19.jpg2015-04-28 13.20.59.jpg
before notice relay....temp panel.....and final new system
 
Last edited:
The installation of that supplementary relay in the top of the first photo is world class ;)
 
Its a classic Andy....they removed the 2 sounder circuits, and connected them to the relay, so the were unmonitored and the silence button or evacuation button didn`t operate.
 
Last edited:
Hi Tazz,

It is a very interesting post and to see that the 'paper work' is right but he installation is not and as you described this as a special needs establishment it does ask questions.
Surely someone must have checked to see that this was ok ad what happened to the routine test of the panel by the staff?

I was under the impression that these places had responsible people and were regulated.

At least you are now getting it sorted.

Best wishes,

Rex
 
Hi Tazz,

It is a very interesting post and to see that the 'paper work' is right but he installation is not and as you described this as a special needs establishment it does ask questions.
Surely someone must have checked to see that this was ok ad what happened to the routine test of the panel by the staff?

I was under the impression that these places had responsible people and were regulated.

The Local Council does have a responsibility, and as such employ this type of Maintenance company to carry out periodic tests and ensure all is installed to standard. And this is were things seem to be going wrong.....the same company look after electrics, plumbing, painting, carpenter issues, emergency lights and fire alarm and general repairs. So not specializing in one area, but all.
Staff such as caretakers are trained to test the system, but you can not expect them to know the ins and outs of the BS5839.
So question is should these companies conduct such tests without being accredited..?
 
Its worrying how often we see this sort of thing. We have just taken a contract from a company looking after a particular councils social housing. Again, all paperwork signed off as all ok yet as soon as you open the panel door or start walking around, its a complete mess.
On a side note, looks like a nice tidy install of that DXc. They are miles better than the old ZX rubbish!
 

Reply to Building Maintenance Company or Dedicated Fire Alarm Company..? in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

Similar Threads

I've asked a similar question before I think and we came to the conclusion that apart from new houses and HMO's etc there aren't any rules about...
Replies
3
Views
333
I am doing renovation to a cafe in Scotland at the moment and after speaking to the local council the building requires the minimum standard for a...
Replies
5
Views
1K
Good afternoon all, Our company installs fire alarm systems in convenience stores but it's always limited to a conventional system whether it be...
Replies
4
Views
2K
Having a bit of a mare at the moment with a small 2 story HMO (6 single rooms with shared kitchen) which was fitted relatively recently (2016 or...
Replies
18
Views
2K
I have worked in the electrical contracting industry all of my life since leaving school over 50 years ago. I started my own electrical...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock