manda

Here's a quick one I want to ask out of interest. I have seen cable running in conduit behind a radiator. Is this considered ok practice due to the heat from the rad when it is on, could this not cause issues?
 
Hi,
has the conduit been discoloured due to the heat etc?
Also, is the conduit running above the skirting board, as in below the radiator, or is it above the radiator ?
I personally would not do it, but I have seen similar and noted a code 4 on the periodic.
Maybe do an IR test to check the condition of the cable.
Hope this helps,
Regards,
Sav
 
It is a where a cable and socket have been relocated so as to fit the radiator, the trunking runs just above the radiator by about 2 inches to the socket. As it is new the trunking is not discoloured. I am not yet anywhere near a spark, so have no intention of messing with it myself, and have no test equip to do an IR test. I was just wondering out of interest really, it just seemed a little dodgy in my view and could have been re-routed along the top of the wall and down to the socket quite easily as the socket had also been relocated. It's in my mums flat, so no doubt when I'm further along I will have a more educated look at it. It may well be that it's ok, just that it didn't seem the best option to me and wondered about the proximity to the rad. : ?
 
Well, like I said, I wasn't sure so just wanted to ask out of interest really. looks dog rough, but then it's a council property so guess they not bothered. ;)
 

Reply to Cable behind radiator? in the Australia area at ElectriciansForums.net

Similar Threads

I've pretty much sussed out the wiring for the radiators and underfloor heating, thanks to help from the forum. I do have one more question...
Replies
6
Views
663
I see they're introducing a new type of flat twin cable with a sheathed CPC. In my location there's no requirement to sleeve CPC/bonding...
Replies
21
Views
2K
Hi all looking for some helpful advice I'm an Aussie so go easy on me, I have a good mechanical engineering head but first time plumbing and...
Replies
32
Views
2K
Hi there - good site. Mrs wants a new socket directly below a light switch on the ground floor (says it will look neater vertically inline)...
Replies
4
Views
1K
What's best practice if running cable from garage out to outside double sockets? I'm re rendering that wall and thought it'd be nice if I could...
Replies
5
Views
771

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock