Re: Calculate the min size of cpc giving consideration to disconnection times and the

Couldn't you just find your maximum demand and look in the bgb for what size cable can carry this safely and then do your volt drop calc to check volt drop if it doesn't comply then go to next size cable and do the calc again and so on, as for the 50kA fault current a type b BS EN 60898 only has a breaking capacity of 6kA or 10kA so you would have to change this for your fault current size why not use a BS 88-2 fuse as these have a breaking capacity of 80kA then do the adiabatic to find your min cpc
 
Re: Calculate the min size of cpc giving consideration to disconnection times and the

Yes, I've done all that, but I was struggling with thermal constrains because we were told to use the diagrams, but actually it was easier with adiabatic equation. I just had to use t = 0,1 s for the calculation.

About PFC I'll try to re-read again few more times. Maybe this time I'll understand it better.

I still don't know about grouping factor, why it says as a note that it can be used only for equal loads, but we use it for different loads how do we choose it exactly - by the circuits or by the cable, because three-phase is not one cable!?
 
Re: Calculate the min size of cpc giving consideration to disconnection times and the

Id like to say that it's nice to see somebody trying their homework themselves, rather than just posting a question and expecting an answer.
the PFC for a 3phase system will be roughly 1.732 x the highest PEFC on one phase. So if you divide 50 kA by 1.732 (in the absence of more reliable data) then this will give you a lower PEFC from which to size your CPC. As a general rule, the higher the fault current, the lower the disconnection times and the smaller the CPC.

as has been mentioned, if you can get a cable size and distance between the supply tx and the main intake postition of the installation, this will allow you to get a lower PFC.
in the real world calcs like this can save thousands of pounds of oversized and over engineered switchgear.
 
Re: Calculate the min size of cpc giving consideration to disconnection times and the

Thanks. I just really intend to practise that profession and I would like to know exactly what I am doing.

Well I calculated the fault current using - I[SUB]f[/SUB] = U[SUB]o[/SUB] / Z[SUB]s[/SUB] .. But I'm curious now what kind of PFC is 50 kA? If using the given formula calculated PEFC for the relevant circuit, can we say the 50 kA is for the whole installation and does that mean we have to use its value (50 kA) for calculating circuit protective conductors or it is necessary just for establishing the rating of the main protective/disconnection device?


PS: When you divide 50 kA with
√3 do you mean finding the phase current from line current (delta 3-phase)? What are main areas of use for delta and star connection. I thought star is more for machines...
 
Last edited by a moderator:
Re: Calculate the min size of cpc giving consideration to disconnection times and the

Thanks. I just really intend to practise that profession and I would like to know exactly what I am doing.

Well I calculated the fault current using - I[SUB]f[/SUB] = U[SUB]o[/SUB] / Z[SUB]s[/SUB] .. But I'm curious now what kind of PFC is 50 kA? If using the given formula calculated PEFC for the relevant circuit, can we say the 50 kA is for the whole installation and does that mean we have to use its value (50 kA) for calculating circuit protective conductors or it is necessary just for establishing the rating of the main protective/disconnection device?


PS: When you divide 50 kA with
√3 do you mean finding the phase current from line current (delta 3-phase)? What are main areas of use for delta and star connection. I thought star is more for machines...


yes and no.

a lot of machines start in star then swap to delta when they are upto speed etc.

there are different types. e.g. star motor, delta motor, star start and delta run

capacitor start, capacitor run etc (capacitor run is for single phase motors)


forgive me if im wrong but you dont normally get a neutral in delta but you do in star

this shows star and delta but not the earth
3phase-isolating-delta-star.jpg


as you can see below, the neutrel and the earth come from the centre (star point of the transformer)

restricted-earth-fault-03.gif
 
Last edited:
Re: Calculate the min size of cpc giving consideration to disconnection times and the

Three phase current is calculated by P/ 1.732 x V x PF

single phase = P/ V x PF

for rotating machines you also have to apply a derating for efficiency.

The above equations show why you need to divide phase to phase current by 1.732
 
Re: Calculate the min size of cpc giving consideration to disconnection times and the

Thanks guys :) I found the chapter in my book for motors and generators. I'll read it first and be more prepared before asking about these systems :)

Back to the thread, one last thing - I'm a bit confused about applying the grouping factor in choosing the cable size. The table in BS 7671 says it is for circuits and cable running together in let's say trunking. So there are 2 things that bother me:

1 - How do we choose the number of circuit/cables when we have let's say 4 circuits, but 3 of them are 3-phase and one is single phase? Do I have to look at the column number 4 or 12 (3 x 4 + 1 x 2)?

2 - There's a note under the table saying that table is only applicable for equal loads! So what do we do in all 4 circuits have different loads?

Thanks
 
Re: Calculate the min size of cpc giving consideration to disconnection times and the

It goes by the number of circuits, it doesn't matter about number of phases.

if you have cables that are carrying less than a certain percentage of their rated current carrying capacity (after derating) then they can be ignored for grouping, but still must be accounted for when sizing the containment.
 
Re: Calculate the min size of cpc giving consideration to disconnection times and the

Thanks johnboy and thanks for the help guys :)
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Calculate the min size of cpc giving consideration to disconnection times and thermal
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
28

Advert

Thread statistics

Created
JuniorSparky,
Last reply from
JuniorSparky,
Replies
28
Views
14,718

Advert