Discuss Can I use the sheath of the SWA as the CPC in this example? in the UK Electrical Forum area at ElectriciansForums.net
HappyHippyDad
Morning..
I have a garage fed by 4mm, 2 core SWA. It is a 25m run from the CU. Can I use the armour as the CPC? The Main house is TT.
I have always used 3 core so have not come across this before. i am about to check my notes as I know I have information on this and will find the formula to work it out but I wanted to start a thread as well in case I miss anything.
Cheers.
Morning..
Cheers.
Re. thread title, no, you cannot use the sheath as a CPC, it's plastic.;)You also ask about the armour, which might be possible. Does anything in the garage require bonding?
Your first line worried me a little then :D
Nothing requires bonding.
I have now had a quick read and it looks like I need to use the adiabatic to find S. I then use Table 54.7 as the protective conductor is not the same as the line conductor.
That makes sense but do I use 0.1s for t as this is a TT and the RCD will be used for fault protection?
I have also read this article.
Using the armour of SWA[1].pdf
The table on page 4 suggests it will be fine to use the armour for a 4mm cable. However, how do they arrive at there figure of 9.0 in the column for min CSA of SWA as they do not have a Ze or t?
  • Using the armour of SWA[1].pdf
There is a table in either the ODG or BS7671 relating to the size of steel armouring to CU CONDUCTORS
Manufacturers produce two core cable so you would have to assume in most if not all circumstances that the armour is adequate for use as a cpc. You have a TT system so the chances of it not being adequate is slim to none. Of course you should prove this and disconnection times are 1s for distribution circuits and 0.2s for all other.
That table has been doing the rounds for years, and is only partially correct at best.
It uses the table 54.7 method to determine the required size of cpc.
With regards that table... How can he just give a fixed 'yes' or 'no' dependant solely on the CSA of the cable (and the amount of cores)?
The table he bases it on 54G is now table 54.7 on page 198 of the BBB. That table uses the value of K1, K2 and S (assuming the CSA of the line conductor is <16mm as in my example). All of these are variables not constants so you cant give fixed values based solely on CSA of the conductors of the SWA.
For example... K1 and K2 vary depending on the cable being thermoplastic or theromosetting and even more of a variable is S as this depends on I and t??
Edit... I've read the tables a little more now and see there are different tables for thermoplastic/thermosetting etc so that just leaves S?
Apologies if I’m hijacking @happyhippydad, isn’t there a certain swa cable size that most all cables under that size would comply for use of swa armour as cpc?....
Two core, 120mm starts to become the size where Table 54G may not be complied with. The three and four cores are larger than that but without looking can't remember.
S is the CSA of the line conductor so is the value you are using as the basis for the selection of the CPC.
None of my wholesalers stock 2core SWA. Seems to suggest the lack of understanding of the use of armour as cpc is widespread...I got funny looks asking for 2 core, turned into a sheep and use 3 core with sleeving!
Reply to Can I use the sheath of the SWA as the CPC in this example? in the UK Electrical Forum area at ElectriciansForums.net
Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Was having a poke around the old man's house today. Anyway. DB is under stairs (18th ed following a recent extension. Not done by me but it's...
Evening all, Having a debate with a colleague about using the SWA armouring and a separate conductor both as CPC's for a circuit. So in theory...
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Been looking at a CU change in a small office and would appreciate comments on the following. Office is supplied from the mains intake in the...
6K