If there is no danger of damage to the S.W.A then I think that it is fine to use it as a c.p.c.
Be careful though, I seem to recall that the total csa of the individual steel wires on some sizes of S.W.A , multiplied by the resistivity of steel etc. is not adequate to be the sole means of earthing. I think that all the sizes up to, but not including 120mm2 are fine. The problems start with the larger cables.
I have never asked, but maybe if you were interested ,the manufactures might give the required details. Cheers.
 
Lenny that is brilliant. I've been looking for something like this for ages, where did you get it.

In reply to Amp David, I think people who don't really know how to make glans off are the ones against it. Yes it's good practice to run a seperate earth but it's not always practical.

cheers, Ron

But surely,if you can run the armoured,you can run a separate earth alongside it,then use both,double back up...???

Sorry Ron..Werent meant to quote you...
 
Last edited by a moderator:
To me providing you calculate using the adiabatic equation as in reg 543.1.3 then using the armour is an acceptable CPC and it even gives it in the reg 543.2.2 (v).

This seems to be a modern development same as not using conduit or trunking as a CPC, it is regarded as safer to run a seperate CPC. I have to admit that in most cases now I do in fact run a seperate CPC, I think most design engineers, unless there is a costing reason, design containemnt systems and SWA with the seperate CPC.

I think even most schemes advise that a seperate CPC is used. It is going with the flow I suppose, and certainly the sparks who trained me would be spinning in their graves to hear that seperate CPC's are run, but sometimes I think you have to go with that flow, rather than fight against it.
 
i've been trying to clear this up(for myself)

there is no reason not to parallel the armour and separate cpc is there?-for SP and 3P SWA on PME

thanks
 
i've been trying to clear this up(for myself)

there is no reason not to parallel the armour and separate cpc is there?-for SP and 3P SWA on PME

thanks

The separate cpc must be sized as if it alone were to take the earth fault current, it is not permissible to add the CSA's of the two conductors together
 

Reply to Can we use the armour of an SWA as the CPC??? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
603
Hi, someone has ordered Steel Tape Armoured cable instead of SWA. Can I use this armour as a CPC the same as SWA or not and if so is there a table...
Replies
13
Views
1K
Evening all, Having a debate with a colleague about using the SWA armouring and a separate conductor both as CPC's for a circuit. So in theory...
Replies
7
Views
1K
Armoured cable or equivalent to go around garden border for on the ground flood lights everyone using any alternative to swa, will H07RN be OK or...
Replies
5
Views
736
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock