Deleted member 26818
At the end of the day, it's your flat.
If you want to do something which doesn't comply that's your choice.
It will only become a problem if you forget where the cable is run and bang a nail into or screw something into the cable. Or if you sell the place, rent it out and the new owner or tenant does it.
There's no requirement for you to notify this work, so Building Control will not know about it and will not issue an improvement notice.
Whilst RCD protection may make things safer, it is not a acceptable method for complying with the Regulations.
So your options are:
Re-run the cable on the surface of the ceiling,
Re-run the cable using a cable with an earthed metallic sheath,
Re-run the cable, chasing it into the ceiling to a depth greater than 50mm,
Provide mechanical protection for the part of the cable that is plastered over,
Re-run the cable in earthed conduit and plaster the conduit into the ceiling,
Hope that nothing goes wrong.
If you want to do something which doesn't comply that's your choice.
It will only become a problem if you forget where the cable is run and bang a nail into or screw something into the cable. Or if you sell the place, rent it out and the new owner or tenant does it.
There's no requirement for you to notify this work, so Building Control will not know about it and will not issue an improvement notice.
Whilst RCD protection may make things safer, it is not a acceptable method for complying with the Regulations.
So your options are:
Re-run the cable on the surface of the ceiling,
Re-run the cable using a cable with an earthed metallic sheath,
Re-run the cable, chasing it into the ceiling to a depth greater than 50mm,
Provide mechanical protection for the part of the cable that is plastered over,
Re-run the cable in earthed conduit and plaster the conduit into the ceiling,
Hope that nothing goes wrong.