How all,

Doing a commercial kitchen with fans above the gas cookers , there is a solinoid gas value that opens the gas when the fans kick in, does this have to be wired on a dedicated circuit , there is a socket right next to it . Board is quite far away .
Cheers
Grand
 
How all,

Doing a commercial kitchen with fans above the gas cookers , there is a solinoid gas value that opens the gas when the fans kick in, does this have to be wired on a dedicated circuit , there is a socket right next to it . Board is quite far away .
Cheers
Grand

Wouldn't how this is wired all depend on the results of a risk assessment?
 
Can’t supply that off a local socket. Any safety systems including solenoids for gas shut off valves need to be controlled by specific control measure for that system. Also you would probably need to incorporate Fail safes etc.
 
I think the OP is asking whether a gas interlock panel and system can be supplied from (e.g.) a fused spur from a socket-outlet circuit, or whether a dedicated radial needs to be run from the DB. I would defer to the specifier of the system as they will be responsible for demonstrating compliance with BS6173 etc. FWIW the load is trivial, a fraction of an amp, other than for the fans themselves.
 
I have seen them wired both ways, personally I would use a dedicated circuit. The supply isn't a safety system as such, if it were it would have some kind of battery back up and be wired using fire retardant cable. Loss of the mains supply would merely default the gas solenoid to close, in a safe position.
 
Is this being controlled by an interlock system to prevent a gas supply if the extraction is off or if the extraction system fails.
 

Reply to Circuit for a gas solinoid valve in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have just had my kitchen redone and the kitchen rewired with a new 6mm cable installed for an electric cooker. However I have changed my mind...
Replies
10
Views
2K
Hi All, We have an old Country villa in Spain. The housing electrics were not good so the house recently has been completely re-wired to a good...
Replies
2
Views
744
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
707
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
274
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock