As long as the CPD is selected to suit the smallest CSA then there is no reason why CSA cannot be reduced as a circuit progresses.
A common example is factory lighting, running say a 6mm leg from the DB to the first point to combat volt drop, perhaps reducing to 4mm or 2.5mm eventually. In this case, the current carrying capacity of the lowest CSA would be taken into account.