Discuss CM500 2 wire testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
J
jason_exact
I have a Megger CM500, just back from calibration so its working! I want to carry out an RCD test on the RCBO on a oven circuit but the tester only has a 2 wire test leads and a moulded plug set of leads for sockets. How do i test the circuit with only 2 wires?
I did phone MEgger and they said you can but i have forgotten what they said to do!
Also how do you carry out a Zs test on the same circuit with only 2 wire set of leads?
This is my first post on here so all help welcome please!
Is there not a 3 wire test lead available to purchase?
Seems odd that it has no trip function with only a 2 wire lead set as i think it uses 25A test current.
Maybe check the Megger website?
thanks
there might be a 3 lead, but im testing tomorrow morning! just trying my house at the moment!
Ever done any 2 wire RCD or Zs testing?
You cant do 2 wire RCD testing as far as i know.
2 wire Zs test is between live & earth only but its test current is around 25 amps and will take out any most MCB's under that.
You really need to try and get the 3 wire set to be able to perform the no trip loop test.
im pretty sure it does 3 wire testing as well but i dont have the leads for it. Also when i spoke to megger they said i only needed 3 wire for phase rotation 3 phase testing. They said you can test the rcd on radial without sockets on with the 2 wire but i cant remember how.
have tried a couple of ways but nothing working.
thanks people, if all else fails look at the manual!
all sorted.
the 2 wire does work for the Zs test black clamp on earth red clamp on live.
the 2 wire rcd test works when you press the type button on the tester to change it to the dc sensitive option.
Hopefully will work tomorrow on the job.
cheers anyway!
A Zs test is between the line conductor and the cpc, A rcd test creates an imbalance between either of the live conductors and cpc therefore why do you need or want a three probe test ?????
line - cpc , trust me it will work.
Reply to CM500 2 wire testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Hi, So I have decided to sell my Megger MFT1721 - See photos below. Originally I bought this for when I was doing my C&G 2391-52 course & then I...
Hi guys, We’ve had a new CNC Machine from China arrive this week. It came with a monitor and a tower to run the software. The monitor and tower...
Forgive me if this is easy to search - I was not able to find anything obvious here or on YouTube. I've got an outdoor circuit that has failed...
I got a TEXT message (i dont know them and i cant find out who they are from the phone number) "Hi speaking from Indeed Are you available to give...