May seem like a stupid question but I have come across a number of commercial installs such as offices, sports centres etc where the installer has used steel conduit which is embedded into the building fabric. As a result rcd's/rcbo's are not generally required on the lighting circuits.

I'm trying to work out why they wouldn't just plaster over the cables and fit an RCD or rcbo to the circuit. Surely it would be cheaper than using steel conduit everywhere.

The only reasoning that I can think is that if that there would be much less disruption caused if someone drilled through a cable and also by not fitting an RCD/rcbo it alleviates the problem of nuisance tripping.
 
It's all about working to specification. The ideal installation is to be done in steel conduit, embedded. Can't get much better.
 
Public or important buildings in many instances. Look at hospitals, fire stations, SPORTS CENTRES, etc. As few problems as possible and the safest installation are required.
 
Driver man that's correct however like Ipaf says socket outlets used for portable appliances up to 20amps require RCD protection. Lighting circuits and such like are omitted from RCD protection if the installation is under the control of skilled and competent persons ie a maintenance guy. My point is why not just fit an RCD and not have to bother installing conduit.?
 
Hi,

I have worked with some very good Architects and not trying to question your thoughts but any good spark would know the answer to the question you are posting, and would regard that type of installation to be one of the best for a lot of good reasons.

Regards.
 
To the O.P
In a house then why not just clip flex on top of the plaster?
Why bother hiding it.

Why do they use doors costing over £1k in some commercial buildings when a B&Q £30 special would still fill the hole?
 
Hi,

I have worked with some very good Architects and not trying to question your thoughts but any good spark would know the answer to the question you are posting, and would regard that type of installation to be one of the best for a lot of good reasons.

Regards.

Must make me a bad spark then.
 
Hi,

I have worked with some very good Architects and not trying to question your thoughts but any good spark would know the answer to the question you are posting, and would regard that type of installation to be one of the best for a lot of good reasons.

Regards.

Not best price though ad I am sure you are aware In this day the cost of an installation is one of the major factors that determines the type of install. I'm not asking of justification I was looking for reasoning why steel conduit may be better not just cos some architect specs it. I was looking for reasons why anyone would spec it.
Thanks for your help guys.
 

Not quite the same is it. Now you are being silly aren't you.

Flex would be visible wouldn't it you silly boy. Customers don't want to see cable clipped surface.

In OP the cabling is hidden, nobody would see it I'm asking what benefits would there be if steel conduit was used.

PS I'm sure the fire regs may pay an important factor regarding the type of door.
 

Reply to commercial installs in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

hi all come across a new build commercial office where radial circuits feeding electrak power track was protected by 32A RCBO at dist board and...
Replies
15
Views
998
I decided to get solar panels, the inverter instructions say one can use type AC, so the existing 14 x RCBO CU seems OK, may be a good idea to fit...
Replies
4
Views
1K
Hi, plumber here so please be gentle (or take the p-ss ;) ), I am supposed to be installing a UV water steriliser for a customer. I have some...
Replies
16
Views
2K
Hi there , Currently doing a college project where i need to select protective devices for the contract. I'm now at the point of selecting SPDs...
Replies
5
Views
2K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock