Hi
So converting a 6mm cooker connection point into a 13a unswitched fuse spur with the load being a 2.5mm pre wired cable from a oven .

is this suitable?

thanks
sid
 
Hi
So converting a 6mm cooker connection point into a 13a unswitched fuse spur with the load being a 2.5mm pre wired cable from a oven .

is this suitable?

thanks
sid

Be better having switching for isolation.
 
What's the rating of the oven? Not a fan of running things through a 13A cartridge fuse if there's likely to be a load of approaching the full 13A for any length of time.
Would be better to reduce the 32A protection device in the CU to 20A or 16A, and fit a DP switch* for local isolation.

*This can probably be the existing one
 
  • Like
Reactions: R-fur

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
bristol
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Convert 6mm cooker connection point to 13a fuse spur for oven
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
2

Advert

Thread statistics

Created
sid521,
Last reply from
brianmoooore,
Replies
2
Views
2,491

Advert