See attached photo of my new 3 phase supply at my house. Tails supply a Schneider 3ph board. Sparky is in two minds about the correct earthing method as the powergrid haven't supplied an earth. What's the correct method?

1000109126.jpg
 
I would ask the supplier why they didn't supply a earth, it looks like you may have to TT the system, but the Electrician should at least enquire about this, also the earth at the bottom looks pretty small so I am assuming it goes to a rod and not the DB, My eyes are not great these days mind but the earth is 6mm2 at best to my eyes
 
As MDJ said. The DNO are not obliged to supply an earth, they normally do but sometimes they don't if they think their system is not suitable or if they think the installation is not suitable for TNCS.
 
Looks like there's phase reversal going on there as well to correct (one hopes) miswired conductors inside the head??
 
Is this a new installation as pencilled labels behind tails from cutout - R Y R N?? Usually marked - L1,L2,L3+N (SSE do).
 
Is this a new installation as pencilled labels behind tails from cutout - R Y R N?? Usually marked - L1,L2,L3+N (SSE do).
I spotted that as well and wondered what that is all about - R Y B, maybe, if the fitter was proper old school, but that makes no sense at all.
 
To the OP, I would ask the sparky to measure the "Ze" using the neutral and a phase.

If it comes out low at 0.35ohm or so, then ask the utility for the earth - most are trying to deliver PME when they can, so might be an oversight.

If it comes out much higher then this that would be why they didn't provide an earth (they aren't actually obliged to do so), so clearly a earth has to be provided by the sparky meaning a TT system, in which case the sparky may need to redesign parts of the installation.
 

Reply to Correct earthing method for house? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good morning all, I am currently working on a House in Multiple Occupation (HMO) consisting of 10 flats, with three parking spots equipped with...
Replies
9
Views
536
Evening all, I'm relatively new to the trade and have just moved house. Looking to rewire and was looking at a few things, could someone tell me...
Replies
10
Views
411
Hi, Posted here as I'm not an electrician, not because it relates to anything I'm considering "Doing Myself". My late parent's house is supplied...
Replies
5
Views
244
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
Hi all, Hope you're keeping well I'm currently wiring a small commercial premises. 3 phas incoming supply, 16sq cables As it is in an urban...
Replies
3
Views
284

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock