I admit this is more complicated that I thought, and this has been a good wake up call!

Now the older cable has been pointed out I do think it might be better to rewire it, as suggested a long time ago.

It might also be possible to just crimp two of them, dispense with the 3rd, and run to a dual plate.
 
A Knightsbridge 60amp junction boxes are much better than what you have but are not maintenance free/screwless terminals. I would use them in a loft when extending electric showers.
Yes, there are a few 60A rated boxes with cable clamps that should take those cables, but as you say they are not MF so would need to be kept in an accessible location.
 
It might be better to look at extending the supply cable using the correct size crimps and heat-shrink, and then putting any junction in an accessible location, or better still having it join at points such as cooker switches, etc.

However that would need proper crimp tools, etc, so really you would be better to get a professional in to do it.
 
So you are adding a third cable.
 
It might be better to look at extending the supply cable using the correct size crimps and heat-shrink, and then putting any junction in an accessible location, or better still having it join at points such as cooker switches, etc.

However that would need proper crimp tools, etc, so really you would be better to get a professional in to do it.
Much as I agree with you I have just had a professional do a part P rewire and this is one of the issues I am left with.
 
A Knightsbridge 60amp junction boxes are much better than what you have but are not maintenance free/screwless terminals. I would use them in a loft when extending electric showers.
It seems your answer wins Aaron as there are no MF products that fit this cable and will certainly be streets ahead of what's there at the moment, thankyou.
 
Status
Not open for further replies.

Reply to Correct way to joint 3 x 30 Amp cables, 30A JB not big enough in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

S
Back to my cat pee soaked floors and a RCBO protected radial cirucit that is giving grief. RCBO symptoms described by the customer, "it's a...
Replies
1
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock