Discuss DB/CU Wylex 3036 6 Way in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
cliffed
Supporter
EICR installation 40 + years old… cabling PVC T&E… no MBPC…
As stated fuses, all ELI measurements are ok… RCD separate from DB/CU 30ma, what’s your feelings on a new DB/CU, installation is in a fair condition.
Classification code recommends C3
Well it is adequate by the key operational aspects (assuming bonding fixed).
However, I don't really like rewirable boards as not that many folks can safely rewire said fuse, both the act of changing the wire for more of the correct rating, and not attempting to remove/insert one in to a live board. In the past I would put in the Wylex plug-in breakers instead as a quick and approved means of avoiding that pitfall.
You could make a case that a CU upgrade would bring some improvement in safety on that front, along with SPD to reduce the risk to any fancy equipment, but it is still a C3 code so really more of advice for the future (e.g. if any new circuit needed, etc).
As far as an EICR goes if it is in satisfactory condition for continued use then that is what goes in the report.
But that doesn't stop you from discussing the merits of upgrading with the customer.
Reply to DB/CU Wylex 3036 6 Way in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi I am carrying out an EICR. I have a garage mini sub DB supplied via 2 x 2.5mm T&E equivalent 5.0mm protected at main DB by a 32A mcb. I know...
Just had an EICR done and C2 (dangerous) applied to 3-way consumer unit which is exclusively for 3 x Storage Heaters. Pic below. Yes its plastic...
Hi all Called to do an EICR on a property 4 studio flats / bedsits within a single house. The t&e sub main to each flat runs within the fabric of...
Afternoon all. Apologies if this is a stupid question. I'm currently half part way through completing 2391 (second exam tonight) - so may be...
4K
Hi. This is a gloriously messy installation I looked at this morning at a house a friend just purchased. It t became quickly clear it was more...