I'm going out later today to quote for installing a kiln in a customers garage.
He has sent me the specs for the kiln and photos of his consumer unit. He tells me that the only other heavy load item is a 10.8kW shower.
The run from the CU to the garage is approximately 25 metres
The kiln is rated at 50 amp / 11.5kW
The CU is split load RCD with 2x 32 amp ring finals, 2x 6 amp lighting and 1x 40 amp shower circuit.

I think the fuse fairy will need to check the DNO fuse size to see if it will cope with the load

I am thinking 10mm2 T&E or SWA depending on routing of the cable
Not sure whether to install separate CU for the kiln (splitting the incomers with Henley block), need to calculate the loads but think this may be better than potentially overloading the current CU.
What would you recommend for connecting the kiln, I initially thought of a commando socket but have only seen them to up to 32 amp.

Any thoughts would be appreciated.
 
I personally would split the tails and use a HRC switch fuse at consumer end with swa cable to a rotary isolator at the kiln end

Note they do make 63 amp sockets!
 
You must do your calculations with the volt drop has well .
 
on the OP's figures, VD for 10mm cable @ 50A and 25m would be 5.875V, so acceptable.
 
No mention of electric cooker in the house, so loadwise it’ll be ok.
Just don’t have a shower on at the same time.

Install a heat exchanger and heat the rest of the house from the garage.
 
  • Creative
Reactions: DPG
another human who wants to recreate ghost!
 
Been out to quote. The fuse fairy tells me there is a 100 amp cut out fuse. The hob is gas and the oven is 3.5kw on a 13 amp plug so load wise I think they will be fine (need to do all the calcs yet)

The only potential issue is the property is a semi on a looped service, theirs being the first. Is it worth discussing with the DNO as I do not know what sort of load the other property will be pulling..

upload_2019-1-18_14-27-29.png
 
do the job first. then let DNO worry if there's a problem. if you contact them first, your client might face a huge bill for modifying the service.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Thoughts on kiln installation in customers garage
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
7

Advert

Thread statistics

Created
PJH2903,
Last reply from
telectrix,
Replies
7
Views
2,271

Advert