What mft are you using and is it in calibration.? Ive never heard of a 240v IR test. You seem certain it is a damaged cable by the screw but test results youve put up would indicate the problem lies elswhere, but you are the one on site so you have the benefit of being there. What was zs at cooker isolator.?
 
What mft are you using and is it in calibration.? Ive never heard of a 240v IR test. You seem certain it is a damaged cable by the screw but test results youve put up would indicate the problem lies elswhere, but you are the one on site so you have the benefit of being there. What was zs at cooker isolator.?

Hard to measure this with MCB banging out
 
Your IR test should show up any issues. However If you can see the Heads of the screws on the new cupboard you could disconnect the cable connect all 3 conductors together and using a long lead check for continuity between screw heads and connected end of cable.
 
To add my morsel;
what history of this fault, did the customer give you?
what range of insulation resistance are you using, 999?
as others have suggested, mcb might be faulty, could you try another mcb temporarily in the CU?

PS, the continuity results, do their correlate with the suspected length of cable?
 
Try IR testing between L and and earth of another circuit, had a fault on lighting circuit where testing cable alone showed no fault but when testing the live to an earth on the rfc it showed a short, turned out new boiler had been fitted and screw had just nicked the live and was shorting through boiler case.
 

Reply to Dead test fail? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
403
Hi all , after some opinions on N-E fault or ring main. After chasing this fault and ruining my bank holiday weekend , ring main IR readings as...
Replies
3
Views
1K
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
648
Hello everyone, I saw in the hospital every circuit has 2 separate cpc, same size, sometimes different. I'm wondering. How we can do the dead...
Replies
1
Views
907
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
659

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock