One of my landlords has an upstairs maisonette which will be changing tenants next week so will need an EICR - I already know there is an issue from a while back which I notified to landlord with a damaged 'Fuse Head'
This is how it used to be ? (Yes, live parts were under the "insulation" tape
So I made good best I could on a previous visit and notified the DNO on the day who were due to attend that night.
I notified the landlord in writing and left it there - but have now found out that the DNO came to look at it and claimed it was not their responsibility.
Since it's prior to the meter, surely it has to be their responsibility? If not, then who's is it?
Anyway, I managed to pop into the lower flat today to have a look.
It's a split dual fuse head from a TNS incoming wire - the old tails go into a pipe in the wall up to the upper maisonette. A fuse head was then installed there, possibly because of distances of tails, (The tails might just be about 3m)
Anyone want to date the tails? No obvious sign of deterioration along the length, but fraying a bit where they leave the downstairs fuse...
I'll try ringing the DNO tomorrow, but since the item in question is before the meter, how would you deal with it? Seems a bit daft to put in a new fused switch there, for the small run to the CU, but I'm also wary of touching the cable pre-meter without something agreed to cover me against claims of meter fiddling.
Pass through Henley Block might be the best option to at least make it safe for now, but future meter installers might well look at that dubiously...
This is how it used to be ? (Yes, live parts were under the "insulation" tape
So I made good best I could on a previous visit and notified the DNO on the day who were due to attend that night.
I notified the landlord in writing and left it there - but have now found out that the DNO came to look at it and claimed it was not their responsibility.
Since it's prior to the meter, surely it has to be their responsibility? If not, then who's is it?
Anyway, I managed to pop into the lower flat today to have a look.
It's a split dual fuse head from a TNS incoming wire - the old tails go into a pipe in the wall up to the upper maisonette. A fuse head was then installed there, possibly because of distances of tails, (The tails might just be about 3m)
Anyone want to date the tails? No obvious sign of deterioration along the length, but fraying a bit where they leave the downstairs fuse...
I'll try ringing the DNO tomorrow, but since the item in question is before the meter, how would you deal with it? Seems a bit daft to put in a new fused switch there, for the small run to the CU, but I'm also wary of touching the cable pre-meter without something agreed to cover me against claims of meter fiddling.
Pass through Henley Block might be the best option to at least make it safe for now, but future meter installers might well look at that dubiously...