An interesting sign has appeared on a local DNO distribution transformer, earths missing from Transformer and HV switch. Is this what is meant by a hot site?
 

Attachments

  • 20200830_190127[1].jpg
    270.5 KB · Views: 59
As far as I know a hot site is one where the resistance to Earth of the earth electrode system is greater than a specified value (2 ohms springs to mind)

What you have there is, as shown by the handmade sign, an abnormal situation, probably classed as a bit of a problem and they might get around to fixing it one day.
 
Probably the earthing has been stolen. I would say that missing earthing is fairly serious and should be fixed as soon as possible.
The HV earth connects the transformer and switch gear to the HV earth mat which is usually separate from the LV earth system. As well as providing a fault return path the HV earth normally has a mat shallowly buried in front of the switch gear so that when you are operating the switch gear your hands and feet are at the same potential in the event of a fault. The switch gear will also have earth switches which are closed to connect the cable cores to earth to make them safe to work on.
 
Probably the earthing has been stolen. I would say that missing earthing is fairly serious and should be fixed as soon as possible.
The HV earth connects the transformer and switch gear to the HV earth mat which is usually separate from the LV earth system. As well as providing a fault return path the HV earth normally has a mat shallowly buried in front of the switch gear so that when you are operating the switch gear your hands and feet are at the same potential in the event of a fault. The switch gear will also have earth switches which are closed to connect the cable cores to earth to make them safe to work on.
The site has been subject to severe subsidance which may have damaged an earth mat, either way as it is the transformer that feeds a large school and some of the kids need hoists and so on, the impact of a earth fault could be very nasty...
 
That is why the LV and HV earths are kept separate. Normally there is eight meters between the two. HV maximum value is 40 ohms, 20 ohms for the LV. However if the combined value is less than one ohm then they can be linked.
 
The site has been subject to severe subsidance which may have damaged an earth mat, either way as it is the transformer that feeds a large school and some of the kids need hoists and so on, the impact of a earth fault could be very nasty...

If it was the LV earth then they would have done a lot more about it than a handwritten note.
 

Reply to DNO transformer + switch missing HV earth in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Has anyone here got experience of doing a soil / earth resistance survey for the design of a large-ish site? We might be looking at a fenced area...
Replies
1
Views
411
Hi all, Would like some advice on the below. Context: Rural French domestic installation TT system Earth rod is situated inside the property...
Replies
6
Views
993
G99 GSI-3 4.4 kw Victron inverter install with EES and batteries and installer can set the export lint if required by dno As part G99 GSI-3 you...
Replies
5
Views
1K
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
523

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock