Absolute rookie error… renovating the downstairs bathroom and drilled a hole in the wall for a shelf, went straight through the cable for the light switch on the opposite side of the wall.

Kicking myself because I actually have a wire detector and didn’t use it.

Spark came out of the hole and all downstairs lights went dark, lucky I didn’t electrocute myself really!

Checked fuse box and the downstairs lights fuse switch was down, flicked it back up to see if the remaining lights would work and it sparked and flicked straight back down again.

My question is can I get away with cutting a hole in the dry wall and crimping the wires and plastering back over? My only concern is that the fuse switch sparked and flicked straight back off, not sure if this means the fuse box/earth could have been damaged and I need to get a sparky out?

Cheers
 
If the protective device won't reset then you have created a short between line/neutral or line/earth or all three.
 
  • Like
Reactions: pc1966 and Dave OCD
If the protective device won't reset then you have created a short between line/neutral or line/earth or all three.
Could this just be severed wire from drilling through it, ie if the wire is reconnected it’ll reset?
 
Don't keep trying to reset it. Make the hole in the wall and show a pic of the cable.
 
Don't keep trying to reset it. Make the hole in the wall and show a pic of the cable.
Haven’t tried flicking it back on since pal, thought best not to try! Attached pictures of the offending cable, thanks for the replies so far 👍
 

Attachments

  • 042B8A19-9A63-4806-82AB-775B194376CF.jpeg
    042B8A19-9A63-4806-82AB-775B194376CF.jpeg
    531.4 KB · Views: 115
  • 0D244C9D-C59C-4398-84C4-62EE901BB5B9.jpeg
    0D244C9D-C59C-4398-84C4-62EE901BB5B9.jpeg
    442.7 KB · Views: 83
Haven’t tried flicking it back on since pal, thought best not to try! Attached pictures of the offending cable, thanks for the replies so far 👍
Whereabouts in Manchester are you?
 
  • Like
Reactions: timhoward
I’ve attached some more photos without the grey protective covering and the light that this powers 👍 thanks guys! I can take the light fixture off to show the wiring directly to the light if needed
 

Attachments

  • 082692DC-74D3-4599-B932-92269B982084.jpeg
    082692DC-74D3-4599-B932-92269B982084.jpeg
    272 KB · Views: 91
  • 627CDDDF-0E52-4EC0-83E7-8CDE1CA875DD.jpeg
    627CDDDF-0E52-4EC0-83E7-8CDE1CA875DD.jpeg
    468.7 KB · Views: 93
Electrician needed. There won't be enough length on the cable to make a required connection.
It's a fair hole through the cable....seen them with red rawl plugs through them and units fitted.😀
 
Electrician needed. There won't be enough length on the cable to make a required connection.
It's a fair hole through the cable....seen them with red rawl plugs through them and units fitted.😀
Thought that might be the case, if only there was an award for an unlucky bullseye!!🤦🏻‍♂️
 
  • Like
Reactions: timhoward and DPG
Can you take a picture of the light fitting which that cable is the switch for too, there might be a simple way to at least get the other lights on again.
Thanks for the reply! Light fitting picture attached 😊👍
 

Attachments

  • EED8B70C-BD75-4D53-B9A3-DA3CF445F326.jpeg
    EED8B70C-BD75-4D53-B9A3-DA3CF445F326.jpeg
    272 KB · Views: 92
Don’t know if it’s worth mentioning that there are actually two light switches to the light fixture (no idea why)

I only use one of them, and I have drilled through the one that I do not use
 
  • Like
Reactions: Jim_e_Jib
Don’t know if it’s worth mentioning that there are actually two light switches to the light fixture (no idea why)

I only use one of them, and I have drilled through the one that I do not use
It is very much worth mentioning. We are close to the limit of what the forum rules allow regarding step by step instructions, for safety reasons.
Take the cover off both light switches. One of them will have two cables in. One of them will have one.
Hopefully the one you do not use has just one.
Post clear photos of the back of both.
 
  • Like
Reactions: DPG
(and I need to go out on a job, so hopefully someone else can take over describing the obvious next step!)
 
It is very much worth mentioning. We are close to the limit of what the forum rules allow regarding step by step instructions, for safety reasons.
Take the cover off both light switches. One of them will have two cables in. One of them will have one.
Hopefully the one you do not use has just one.
Post clear photos of the back of both.
Hopefully I’ve struck lucky! The one I do not use has one, the one I do use has two! Pictures of both attached 👍
 

Attachments

  • 39AA6139-B69A-42C9-80D6-21CFE00FB91C.jpeg
    39AA6139-B69A-42C9-80D6-21CFE00FB91C.jpeg
    351.9 KB · Views: 64
  • 49EEFA2F-C287-4BB5-B3EA-668B41BECA57.jpeg
    49EEFA2F-C287-4BB5-B3EA-668B41BECA57.jpeg
    319.8 KB · Views: 68
Hopefully I’ve struck lucky! The one I do not use has one, the one I do use has two! Pictures of both attached 👍
You did. Turn power off.
At the switch with lots of wires:
disconnect, remove and set aside the wires from the red, yellow, blue cable (that is damaged further along). Cut the very ends off and tape up well.
The leaves you two red wires belonging to the same cable. Connect them to Common and 1, either way around.
Leave all the yellow/green sleeved stuff alone.
Put that switch back together.
Your lights should now not trip.
 
Last edited:
  • Like
Reactions: nicebutdim and DPG
You did. Turn power off.
At the switch with lots of wires:
disconnect, remove and set aside the wires from the red, yellow, blue cable (that is damaged further along). Cut the very ends off and tape up well.
The leaves you two red wires belonging to the same cable. Connect them to Common and 1, either way around.
Leave all the yellow/green sleeved stuff alone.
Put that switch back together.
Your lights should now not trip.
Cannot thank you enough, you’re an absolute star. Worked like a charm!!! Saved me a hell of a lot of hassle and money, all lighting back on! 😊👍
 
While your luck’s in… what’s next weeks lottery numbers?


Lucky twice.
1. Not blowing a bigger hole in yourself
2. Managing to pierce the one cable that was easiest to explain how to disconnect. Hit a red/black and it could have been anything.
 
  • Agree
Reactions: timhoward

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Drilled through light cable
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
21

Advert

Thread statistics

Created
Electricalnoob96,
Last reply from
littlespark,
Replies
21
Views
6,055

Advert