Discuss Dual board rcd tripping in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

M

macloon

Hey there everyone, I have a question hopefully you can help with. A job where ive fitted a new circuit on to the fuse board is having problems with the RCDs. Its a split load board so has the Line and Neutral supply into the 100amp main fuse from there Neutal up to the neutral bar and Line over to a 80amp RCD, from there is a Neutral feed from the same bar as the 100amp neutral and a Neutral to a seperate neutral bar for that RCD and another Neutral and Line that goes onto a 63amp RCD which then has a Neutral going to another bar for that RCD.
When the 80amp RCD trips the 63amp RCD stays up which it should, but when the 63 amp RCD trips it takes out the 80amp 1 to. I dont understand why. Any help would be much appreciated
 
I'm really struggling to visualize what you have described above, a picture as they say, is worth a 1000 words.

If I had to guess, I'd say the neutral from your newly installed circuit, has been connected to a different neutral bar than the one which belongs to the RCD that is protecting it.
 
Sounds like a dual rcd consumer unit(a main switch of 100a and 2 rcd,is the neutral connected to the correct bar in relation to the circuit breaker/rcd 1 or 2.
 
i think his describing a duel RCD board with 100A main switch..
you say when the 80A one trips the 63A stays up but when the 63A trips it takes both out. taking both RCDs out normally indicates a crossed neutral as this will show as an imbalance across both RCD's. have you worked out what is being switched or used to cause the rcd to trip. it sounds like you may have two faults. one crossed neutral (causing both to trip) and one on the 63A RCD causing just that one to go..

Edit im asuming their both 30ma :)
 
Last edited by a moderator:
rcd.jpgyes both are 30mA, nothing is causing a fault it is when I test the Rcds that it occurs which means it will happen if a fault ever occurs.
 
when you say testing the RCDs you mean timer test? or testing a circuit like earth loop?
I would start by doing an IR test between Neutral bars and switch stuff on/ off etc, see if it remains open circuit ( it should) any drop in reading will indicate a resistance across the neutrals which means an imballance across the RCDs this could cause tripping problems even if its not a dead short.. apart from that without more info im stumped
 
Last edited by a moderator:
yes all MCBs are connected with all neutrals going to correct neutral bar. when all are on nothing trips is only when i test the RCDS
 
no i mean just pressing the test button
oh ok,, the test button puts a resistive short between outgoing Line and incoming neutral. maybe, just maybe your neutral on one side of one of the RCDs is at a lower resistance than the incoming neutral, so when you press the test button the easyst path is through the other RCD..
try P-N loop on the load side of each rcd I wonder if it will show better on one than at the service head

ps this is just a theroy and would be intrested to find the outcome.
 

Reply to Dual board rcd tripping in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
329
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
My circuit panel has two banks of breakers, each bank protected by an RCD. One of these RCDs has been problematic in that it trips intermitantly...
Replies
12
Views
1K
I've got a dual rcd mk sentry board that I want to inverter into an rcbo board. If I link the two neutral bars from the main switch is this OK to...
Replies
3
Views
1K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock