Discuss Earth Blocks and Bonding cable underneath kitchen concrete floor in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
tomodo
Hi couple of questions, in the middle of doing a CU change, was thinking to run Bonding cable under kitchen floor to CU, As its a earth cable does it require any protection such as metal conduit ? was going to chase on concrete floor about 3 meters. And doing earth connections next to CU i have ordered a Earth block, is it required to be in a insulated housing? surely it could become live in the event of a fault? cheers
Do you have a copy of BS7671? all the info you require is in there somewhere.
No, although putting it in some sort of conduit would make changing it in the future easier, if required.
No need for an insulated housing. You're not going to enclose whatever the bonding cable is connected to, are you?
Just think about that for a minute and consider conduit, trunking, micc, the bonded extraneous parts, cable tray, ladder etc etc
Then if you still want me to answer that question, put a tin hat on!
Earthed metal conduit for your earth. Now that's a novel idea.
(I know op didn't say that, just a daft thought that popped in my head)
But would it be acceptable to dispense with the earth and just use the steel conduit as a bonding conductor?
(Just a little something to get a trainees brain turning)
I've not got my books to hand but I'd stab a guess that it should OK provided the csa is large enough, and I believe (top of head) it would have to be minimum of 25mm, so chances are unless you're running the next channel tunnel, the answer would be no?
Without any books that's a good effort [emoji106]
To be honest I couldn't give a definitive answer in this case without consulting the books.
But you are right that it could be used if the csa is appropriate, so you would need a steel csa of 85mm to replace a copper csa of 10mm.
This calculation is only for bonding conductors, not for cpc's.
The steel conductor needs to have the same conductance as the required copper csa. Copper has a conductance approximately 8.5 times that of steel. So to convert copper csa to steel csa for main bonds you multiply by 8.5
Reply to Earth Blocks and Bonding cable underneath kitchen concrete floor in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Doing some work in a commercial restaurant/kitchen the builders had already boarded and plastered the walls meaning my only viable route is to use...
Hi, this is a repost of the initial in diy as the only potential diy aspect is the prep ahead of a qualified person attending, this is hopefully...
Disclaimer: I'm not going to attempt this job myself, I want a professional to do this job properly since I consider it non-trivial and need it...
Hello All. I'm quite new to this game and gaining experience, but going well in the main. My customer wants to feed a Hob ( on island in centre...
