Does anyone have any experience in recording values of EFLI on circuits fed through a DB supplied via a UPS please? The meter shows the above scale arrow.
I understand that there will be no reference to the external earth due to the inverter inside the UPS but what will happen to the UPS supplied circuits under fault conditions in normal supply mode? Is this something to be taken up with the manufacturer? Then there is next question how does the UPS deal with a fault in power failure mode? Not to worried about the second part, I obviously need to take some readings of EFLI to record and to see if they are sufficent to meet disonnection times.
Any help would be great.
 
You are only measuring the impedance of the output stage of the UPS.

Record values on bypass and remember that the UPS itself will clear any faults by limiting it's own short circuit current and eventually shutting down-often at around 100mS to protect the inverter and any damage downstream caused by the fault.
 
  • Like
Reactions: 2 people

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Earth fault loop impedance readings through a UPS supply
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
1

Advert

Thread statistics

Created
treak,
Last reply from
IQ Electrical,
Replies
1
Views
12,165

Advert