Discuss Economy 7 immersion heater timer in the Central Heating Systems area at ElectriciansForums.net

Reaction score
0
Hi,

My house is currently on economy 7 as we are fully electric. Our immersion heater has 2 switched one for day rate and one for night rate.

Our electricity bill has been sky high and we have narrowed it down to the immersion heater being heated for the full time when E7 switches on for the full 7 hours. is it possible to install a timer so it only comes on for 2 hours in the morning, or will it reset the timer if I wire it into the E7 circuit.

Thanks
 
the stat should ensure that the heater only works intermittently as the water cools. how well is the tank lagged? my estimate is should cost about £2 /night.
 
what's the kW rating? should be on the element cover label.
 
my earlier post assumed 3kW so about £2/night tops. based on E7 rate of about 3p/kWh.
 
plus that looks like a part l compliant unvented cylnder so as telectrix said the stat should cut in and out, is the hot water hotter than 65 degrees, if it is you could have a faulty stat
 
The norm is to exceed 65°C to avoid legionnaires, at least at some point in the cycle, and with off peak either a manual boost or twin thermostats (some times twin immersion heaters) so whole tank heated over night, with off peak, but should it have heavy demand then upper thermostat/immersion heater will heat a small amount of hot water to keep it going until the next off peak supply.

Some times an attempt to reduce the bill by turning down the temperature can do the reverse, if lower immersion heater is turned down, then upper one more likely to operate, the same if lower immersion becomes faulty. Idea is the water will never be cool enough for upper thermostat to operate.

With a top entry immersion you can get two immersion heaters in one, but side entry needs two immersion heaters. You only show one, so would seem some thing missing?
 

Reply to Economy 7 immersion heater timer in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
806
I am asking on behalf of a friend who has an outbuilding that he uses as an art studio, the building is fully insulated and is currently heated by...
Replies
1
Views
527
I
Hello folks. Just looking for a little help please. Recently I fitted a fst77 timeguard for a single 2.5kw simplex model NLSH18MN. This works...
Replies
6
Views
541
Yesterday moved my Mum into her new bungalow. The Hortsmann had been off for a few months I suspect. The boost worked, but nothing happened...
Replies
3
Views
898
if a house has economy 7, off peak board and on peak board. and where the meter only energizes the off peak board during the night for the storage...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock