Discuss Eddy currents?? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
6
After a bit of advice. Have a 630A MCCB feeding a DB, it's fed with 4 x 300mm single core, non armoured HO7 cables and a 185mm earth. The DB is GRP and plastic compression glands have been used. The main panel has an aluminium gland plate and brass A2 glands have been used, however, the lock nuts are steel. Will this cause issues, do the lock rings need to be changed to brass also?
 
Any metal that completely surrounds a single core cable should be non-ferrous, that includes lock nuts, so in my opinion these should be changed to brass.
Interesting. I hadn't thought of locknuts being subject to eddy currents, but what you say makes sense when I think back to basic AC circuit theory.
 
After a bit of advice. Have a 630A MCCB feeding a DB, it's fed with 4 x 300mm single core, non armoured HO7 cables and a 185mm earth. The DB is GRP and plastic compression glands have been used. The main panel has an aluminium gland plate and brass A2 glands have been used, however, the lock nuts are steel. Will this cause issues, do the lock rings need to be changed to brass also?

Any metal that completely surrounds a single core cable should be non-ferrous, that includes lock nuts, so in my opinion these should be changed to brass.
I have always kept the lock nut the same material as the gland on single core cable, just something I was told years ago but never actually fully knew why. The reason I asked is because they are going to be pig to take back off and swap and wondered whether anyone had any experience of it.
 
I have always kept the lock nut the same material as the gland on single core cable, just something I was told years ago but never actually fully knew why. The reason I asked is because they are going to be pig to take back off and swap and wondered whether anyone had any experience of it.
I’m afraid that’s what needs to be done, especially on high current circuits such as this.
 
It will be easier to replace the lock nut on singles, assuming there is ready access than a multi-core cable.
I agree, multi core would be worse. There is however a plastic gland plate half way down the enclosure which cables run through an additional plastic compression gland for support. The lug probably won't fit through the plastic compression gland so would have to cut the lug off slide it back down through the plastic gland and then swap the lock nuts.

Nowhere near impossible just a lot of extra work, hence wanting a bit of clarity as people have different opinions on it. Would ideally like to leave the steel ones place but obviously wouldn't if its going to be dangerous.
 

Reply to Eddy currents?? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been browsing these forums for a while, always great to learn a new way to skin the same cat. Anyway, cut a long story short, was an...
Replies
11
Views
737
I've an otherwise small and simple job to do later, out of hours, fit an outdoor IP FSU for a small AC unit fed from an outdoor socket on an RFC...
Replies
12
Views
2K
I have a metal Hager sub CU, 10 way RCBO, installed in 2018 in an accessible attic space, this sub-CU being fed from another unit close to the...
Replies
11
Views
6K
Has anyone used a brass gland plate to earth a line of SWA glands e.g. at a DB, and had anyone such as an NICEIC inspection flag it up as...
Replies
17
Views
3K
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
835

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock