I'm doing 30mA & 100mA RCD resting on a TN-S system

TN-S earth fault loop impedance max is .8 ohms
TT earth fault loop impedance max is 200 ohms

Regs state approx 1500 ohms for RCD on TT system

What should the maximum Zs be on a TN-S system when testing an RCD?
 
I'm doing 30mA & 100mA RCD resting on a TN-S system

TN-S earth fault loop impedance max is .8 ohms
TT earth fault loop impedance max is 200 ohms

Regs state approx 1500 ohms for RCD on TT system

What should the maximum Zs be on a TN-S system when testing an RCD?

On a 230V supply Max Zs can be worked out like this:

Max Zs = 50V ÷ IΔn


So for a 30mA RCD the max Zs is 1666.66Ω (50 ÷ 0.03 = 1666.66) and for a 100mA RCD it is 500Ω (50 ÷ 0.1 = 500)
 
The maximum a 30mA can protect at is 1666 as Jud has said however, it should still be below 200 Ohms on a TT and irrespective of RCD protection or not the max ZS on an a TN-S should still be around 0.8
 
The maximum a 30mA can protect at is 1666 as Jud has said however, it should still be below 200 Ohms on a TT and irrespective of RCD protection or not the max ZS on an a TN-S should still be around 0.8

That would be Ze, not Zs.

A Ze or Ra of more than 200Ω on a TT is considered unstable as Caddy says.

The maximum Zs of circuits on a TN system should be taken from Tables 41.2 to 41.4 on pages 48 & 49 of BS7671.
 
devon1, I've just noticed your qualifications in your signature.

With those qualifications you really should know all this ;)
 
devon1, I've just noticed your qualifications in your signature.

With those qualifications you really should know all this ;)

yeah i just need to explain it to the electrical engineer on site! The engineer is telling us that the Zs max is 1500 ohms on the TN-S
 
Last edited by a moderator:

Reply to EFL on TN-S with RCD in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
843
Keeping this brief.....................New dwelling.....TT system with 100mA S type rcd protected supply to local board with 30mA RCD. Freelance...
Replies
21
Views
3K
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
968
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Afternoon all, Got a bit of a strange one (by my usual standards anyway). Job is a large barn conversion, done years ago, there's loads of work to...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock