Hi Chaps,
Had my 3rd assessment on Tuesday ( which i passed) and i was asked why the trip times for the RCD ( x.5 x 1 and x 5) were the same for all circuits.
I said him i was told to test the RCD at the board and record those times for all the circuits covered by that RCD, he asked who had told me to do it this way and i said it was the chap who took my last assessment. He said this was wrong and i should test every circuit controlled by the RCD.

Which way do you do it?
 
The true characteristics of an RCD can only be tested at the RCD with no loads connected.
 
Assessors are like all of us,we dont know it all

In this instance he is wrong

As sintra rightly explained,an rcd has a characteristic that can be affected by connected loads

The rcd does not change those characteristics when different circuits are tested
The circuits themselves may cause different readings because of connected loads
Test at source and apply those results to all protected circuits
 
theyre usually not trying to trip you up or cause trouble, like building inspectors sometimes its best just to nod your head and smile
 
Hi Chaps,
Had my 3rd assessment on Tuesday ( which i passed) and i was asked why the trip times for the RCD ( x.5 x 1 and x 5) were the same for all circuits.
I said him i was told to test the RCD at the board and record those times for all the circuits covered by that RCD, he asked who had told me to do it this way and i said it was the chap who took my last assessment. He said this was wrong and i should test every circuit controlled by the RCD.

Which way do you do it?

I was also told on my fourth Elecsa assessment to do the RCD test the same as you. However i do check the RCd operation at 1x on each circuit just for peace of mind. In his ( the assessor) words it is much easier to find and replace a faulty RCD before all the breakers are fitted and wired up.
 
Great question, I was always taught to test at source only, and the reasoning given was that as long as all previous tests have passed, i.e IR, ohms etc, then you know your circuits are fine so testing RCD at source will only be required to verify RCD is operating correctly.
 
Sintra and Des thanks for that, i did think the same thing but as it was my assessment just nodded in agreement:)

Sometimes they do that just to see how confident you are in your knowledge and judgement. On my first assessment Instead of shorting out at the CU I removed the cables and put them in a choccy he said I should have shorted them out I said no safer this way especially if cables for any reason were forgotten or I fell ill and customer turned supply on. My bottle was going but he just smiled and said yes you are quite correct.


Chris
 

Reply to Elecsa assessment in the Certification NICEIC, NAPIT, Stroma, BECSA Forum area at ElectriciansForums.net

Similar Threads

NICEIC Certification Scheme Getting accredited to
Looking for some advice regarding joining a CPS. I've been in the electrical industry in various roles for nearly 10 years. I started my...
Replies
15
Views
996
Firstly, thank you for taking the time to read this. I am not trained in electrics whatsoever, I am a just a home owner looking for advice. I...
Replies
2
Views
991
Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
797
I got a TEXT message (i dont know them and i cant find out who they are from the phone number) "Hi speaking from Indeed Are you available to give...
Replies
15
Views
888
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock