Reaction score
0
Can anyone tell me the correct way to extend cables. I have seen many people using pre-insulated crimps, and yet they are not supposed to be used on solid core cable.
 
better with wagos on solid cable, but crimps are ok if fitted correctly. i would like to see a crimp whereby the solid cables could be overlapped then crimped.
 
Last edited:
Again, the same Tutor who told me that the neutral bar in a consumer unit is live.
Apparently they cut into the conductor and can weaken the joint. He said they should only be used on stranded cable.
It makes sense, but I know of loads of electricians that use them all the time.
 
Looks like it's 1 all with the tutor. The neutral was right the crimps are wrong. As a use of compression tool is recognised in the regulations, and the regulations does not exclude solid conductors, then it's not only permitable but done correctly there should be no problems.

For repairing a break on a cable in a wall. where running a new cable is just not feasible, then crimping with a compression tool and IMO using heat shrink is the most sensible way to go. If your extending cables inside a control box where there are many circuits then again crimping is perhaps the most sensible way to go, and as it's in an enclosure you may IMO omit the use of heat shrink.

Extending a few circuits on a CU change then I would IMO not use crimps but an adaptable box with klippons and din rail. it looks a much neater jobs and easy for future testing.
 
Many thanks.
So are you saying that the neutral bar in a consumer box is live?
It's just that I had a reply to this in another thread, and I was told that it wasn't
 
Now I'm confused again. If you have time, would you be kind enough to have a look at my thread in the General Electrical category, under Neutral Bar in a consumer unit.
I have various answers on this subject that are different
 
just to clarify. the neutral is the return path for the circuit. as such, it is technically a phase conductor and should be treated as such. the fact that it's potentiual wrt. earth is normally 0v does not make it necessarily "safe to touch"
 
Thanks again telextrix. That all makes sense to me now. The way my Tutor explained it though was obviously wrong. He told us that there was 230v on the Neutral, and he didn't mention any fault conditions which just didn't make sense to me.
 

Reply to Extending Cables in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

  • Question
Hi All. I need to extend the cables for a 3 plate ceiling rose/pendant on ground floor ceiling by 450mm. Can I fix the ceiling rose/pendant to...
Replies
5
Views
400
Thinking of getting a Runpotec XB300 cable dispenser, as my yellow framed tripod thing is unsatisfactory for all the usual reasons. You can...
Replies
8
Views
622
I have Liebherr fridge freezer and need to extend the cable from the appliance to the wall plug. The directions do not allow an extension lead to...
Replies
2
Views
854
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
912
We have had RG11 installed in some flats for use with Virgin/Internet. It should I think have been RG6 but the guy at Virgin was insistent it...
Replies
4
Views
405

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock