sponge23

Hi all, having a problem on a job...
Using a switched FCU to control some LED under-cabinet strip lights. Customer reported that the lights were staying on after the FCU had been switched off. So I thought the FCU must be stuck in on position, so I replaced the unit.
Had a call from the customer today reporting the same problem.
Upon inspecting the original FCU, it appears to be working as it should. I.e. it isolates both live and neutral.

Any ideas?
Thanks in advance.
 
i suspect capacitance . a snubber may help.
 
possible. it's quite common for GU10 LEDs to stay faintly lit or flash after switch off. capacitance or induced voltage from adjacent live cables. a snubber draians the unwanted voltage away.
 
try a 1 watt resistor, value around the 200Ω mark across the ELV feed to the strip
 
Hi all, having a problem on a job...
Using a switched FCU to control some LED under-cabinet strip lights. Customer reported that the lights were staying on after the FCU had been switched off. So I thought the FCU must be stuck in on position, so I replaced the unit.
Had a call from the customer today reporting the same problem.
Upon inspecting the original FCU, it appears to be working as it should. I.e. it isolates both live and neutral.

Any ideas?
Thanks in advance.

My idea is that it may have been wise to test the suspected "faulty" FCU BEFORE you went to the trouble and expense of replacing it. ;)
 
To Geordie Spark: I had this problem with an FCU before, admittedly an LAP one. So thought it would be prudent to take a replacement with me and just swap it.
The FCU in question this time is a BG one, which are usually alright.
Had no end of trouble with LAP bits in the past, so will not use anymore!
 
Snubber's are usually capacitors not resistors.

they're usually a R-C combination. anyway, as i advised the OP, the ELV side is DC, so a cap. would do diddly squat.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
FCU and Led under-counter light problem
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
9

Advert

Thread statistics

Created
sponge23,
Last reply from
telectrix,
Replies
9
Views
2,123

Advert