Hi Guys
A first floor flat I rent out requires an EICR. It was purpose built in 1990. I'm no longer in business or up to date with regs and realise that there may be some issues lol.
The meter box and cutout (100Amp) feeds the Main CU and an E7 CU installed in the flat on an outside wall inside a low level kitchen unit -grovelling required for access. The Main Switches were both 63Amp and at some time I changed these to 63 Amp RCDs. The tails look to be 25 sq mm. The Main CU has MCBs and the E7 CU has the original cartridge fuses.
1. The tails are at least 4m long and installed in the wall cavity. Possibly no mechanical protection.
2. I'm told the main switches need to be 100 Amp to protect the cutout. Is this a new requirement?
3. All circuits are off one RCD, but I would argue that that it's a small flat, on one floor, so is not unsafe.
4. Cartridge fuses in E7 CU ok?

I'd appreciate your comments please, and if you have observations, what code would you give?

Cheers!
Pete
 
If you changed both main switches to RCDs hoe can all the circuits be fed from one RCD?
 
1. The tails are at least 4m long and installed in the wall cavity. Possibly no mechanical protection.
2. I'm told the main switches need to be 100 Amp to protect the cutout. Is this a new requirement?
3. All circuits are off one RCD, but I would argue that that it's a small flat, on one floor, so is not unsafe.
4. Cartridge fuses in E7 CU ok?

1. I doubt that will get any comment on an EICR.
2. Main switches do not provide any protection to the cutout, but they do need to be rated correctly for the size of supply. If the supply is fused at 100A then the main switch should be rated at 100A this is just common sense. It's not a new requirement, it has been the same for many, many years.
3. I would expect this to be coded as a C3 at worst.
4. Yes fuses are a complaint OCPD
 
re Item 2. So the original installation was wrong. Should've thought about it more at the time I changed to RCDs! Got so used to buying CUs with 100 Amp Main Switches as standard whether that rating was required or not and never having to question it.
[automerge]1597873036[/automerge]
Unless all mcbs add up to less than the RCCB rating
Hi Matt
I think davesparks is suggesting that's irrelevant? ie. 100 Amp Cutout, therefore 100 Amp Mainswitch.
 
Last edited:
you could kill 2 birds with 1 stone.fit a 63A Switch/fuse after the meter. that will make the 63A RCDs compliant and also protect the CU tails that are over 3m to keep DNO happy.
 
you could kill 2 birds with 1 stone.fit a 63A Switch/fuse after the meter. that will make the 63A RCDs compliant and also protect the CU tails that are over 3m to keep DNO happy.
I would need 2 Switchfuses as it's E7. I'm doubtful that there's room in the meter box for 2 switches. If you cost fitting 2 Click DB750 switchfuses against supply and fitting new RCDs, the latter wins hands down!:) I think that the slightly too long tails may not be noticed! I'm also thinking that 63 Amps could be considered a bit tight on the load side so these 100 Amp RCDs will remove that discussion.
 

Reply to Flat about to be EICRed in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
827
Hi all Called to do an EICR on a property 4 studio flats / bedsits within a single house. The t&e sub main to each flat runs within the fabric of...
Replies
4
Views
2K
Trying to organise a CU replacement at home. It's a 1930s property. It's got a 10way CU but with no RCD protection. Was after a larger unit with...
Replies
65
Views
4K
Can someone sanity check my thinking please.... An 80 amp PME service head, tails to meter, 25 sq mm tails into an enclosed fused isolator with...
Replies
4
Views
1K
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
274

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock