Hi I have a flat down neutral to earth fault on a kitchen ring rcd isnt tripping and I have 30+megohms on the other ir tests! There is.extractor fan in the kitchen that has no fcu
What is the reading for the IR test N-E? are your tests carried out with the RFC conductors sill connected to the CU?
Would an extractor fan bring the readings between n-e down just thinking they may have spurred it off and im reading through that
I have isolated the leg thats down split the ring and put it on 2 20amp breakers so I can leave it safe till Monday!The leg thats down seems to run close to tge extractor looked inside and there is 1 x1.5 but no sign of a fcu so assumed it was part of the lighting circuit! If it has been spurred off the ring could this give me the strange readings
So you have identified the faulty leg, how do you plan on testing the RCD as that also needs to be replaced of there is a fault with it.
Reply to flat down neutral to earth reading in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Having a challenge understanding the concept behind why when you measure across line and neutral (live circuit) using voltage indicators we have...
Hello everyone, Hope you're all well. I'm carrying out an overall/global insulation resistance test on a newly wired 3 phase installation we did...
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...