Hi all looking for some advice working on a job adding on a couple of sockets and spurs for w/m.& heat / co alarm to existing c/u in garage which is getting supplied by 10mm t&e from house c/u on its own garage c/u 40a mcb anytime the washing machine gets used it is by passing 12way wylex c/u and tripping the garage c/u in the house all circiuts are testing fine iam lead to believe the 10mm T&E is undergroud in ducting everything is working fine until put some kingd of load on ie w/m kettles .any ideas would be much appreciated thanks.
 
What's tripping? MCB or RCD.

Could possibly be a loose neutral on the supply side but that's a pure guess.
 
What's tripping? MCB or RCD.

Could possibly be a loose neutral on the supply side but that's a pure guess.
What he said
 
Hi all looking for some advice working on a job adding on a couple of sockets and spurs for w/m.& heat / co alarm to existing c/u in garage which is getting supplied by 10mm t&e from house c/u on its own garage c/u 40a mcb anytime the washing machine gets used it is by passing 12way wylex c/u and tripping the garage c/u in the house all circiuts are testing fine iam lead to believe the 10mm T&E is undergroud in ducting everything is working fine until put some kingd of load on ie w/m kettles .any ideas would be much appreciated thanks.
Can't make any sense of your post, might make more sense if you post a diagram of what you have
 
  • Like
Reactions: DPG
Are you saying there are RCDs in the garage AND the house? If so, then it's not that anything is 'bypassing ' anything, it's just that with 2 RCDs in series there is every chance that both will trip. Apologies if I've misunderstood.
 
This is the important bit. If heavy loads cause a trip, especially if the load is not on the RCD that trips, it suggests an N-E fault downstream of the RCD.
There is no RCDs on either board Just main switchs and Mcbs the house one is the only 1 that trips the 40amp mcb it by passes the 1 in the Garage cheers.
 
I think a picture of each board would help a lot here

Also how are you adding new sockets without an Rcd in place and making it complient?
 
  • Agree
Reactions: DPG
I think a picture of each board would help a lot here

Also how are you adding new sockets without an Rcd in place and making it complient?
The Main switches are getting changed to Rcds the Garage 1 is a wylex 12w split board and the house 1 is Single main switch and 1 40mcb this is the orignal installation thats Tripping before i update it cheers.
 
Pictures?

MPS nobody is trying to trip you up here. It would truly be useful
 
I assumed RCD tripping also. Didn't think it would be the 40A MCB.
 
I attended the exact same fault a couple of days ago. Two faulty sockets, replaced, fault disappeared. While it was ok with low draw things anything like a hair dryer of hoover tripped the MCB. Two different socket circuits doing the same thing. Cheapo sockets, arcing due to loose connections in the socket, pays to buy quality.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Garage c/u Tripping in House
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
13

Advert

Thread statistics

Created
JoeBloggs,
Last reply from
Wilko,
Replies
13
Views
2,052

Advert