Hi all,

I have been practising my testing at my parents house as I'm still an apprentice.

Just a quick question. The garage, which is separate from the house has been spurred off the ring main with an SWA. The cable run is approximately 5 metres and is terminated in an isolator in the garage. The isolator then feeds a double socket and FCU for a light.

The ring is protected by an rcd.

Is this acceptable?
 
i think what he meant was .... is the SWA properly glanded and the armour earthed. this is usually acheived by coming from the socket in T/E and connecting into the SWA in an adaptable box on the outside of the house wall.
 
Sorry misunderstood.

There are no signs of boxes or FCU and it is not fed from the socket nearest the cable entry. Therefore, I can only assume it has been put in a junction box under the floorboards. Not good!

The armoured is 3 core so has an earth and the earth loops are fine but I doubt the armoured itself is earthed.

What code would that be on a report?
 
Easy way to check if the armored is earthed, Do a R1 R2 test between the line and the armoring :)

Thanks, will do that.

Is it dangerous if its been spurred off the ring circuit in a junction box?

It's been like it since my parents moved in and have never had a problem. It is also protected by the RCCB at consumer unit.
 
It should be fused down really in case someone tries to extend the circuit in future or overload it.
We cant tell you if its safe or not but if its been done properly there will be nothing wrong with it although its not the way I would do it!
 
Ok thanks.

If its not earthed then I will put a properly gland on and earth the SWA.

It will then supply one Rcd socket and one spur for the light fitting.
 
As you earlier stated that the ring from which it has been spured is RCD protected there is no need to install an RCD protected socket outlet in the garage (assuming that the installed RCD has an operating current of 30mA). Indeed, to do so will be non-compliant with BS7671 as there will be a lack of discrimination between the series-connected RCDs.

I would expect to see a 13A fused connection unit on such a spur at the feed end and for practical purposes I would always install a 2-pole isolation switch at the house end in case there is any need to take the external circuit out of service (best combined as a switched FCU).

Lighting in the garage should be via a 3A FCU.
 

Reply to Garage spurred off ring... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Replies
11
Views
737
Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K
Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Replies
4
Views
896
Evening all, Been to a job on Fri where the customer had a condition report completed. Two of the remedial identified was that there were too...
Replies
7
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock