flashy5313

EF Member
Hi all,
I am looking at installing one of these puppies, I am thinking RCD FCU would be required. Any views or possible alternatives. Re wireable fuse situation.

Thanks in anticipation
 
Last edited:

Rockingit

Forum Mentor
If you've not got RCD protection on the lighting already, your bonding is sorted and it's out of zone, then yes, basically.
 
D

Dave 85

Yeah RCD FCU prolly cheapest way to go. You don't wanna stick it in the loft though. I sometimes just put one under the C/U to cover the entire circuit.
 

Guitarist

Electrician's Arms
If you undertake any work in a room containing a bath or shower, all circuits must be RCD protected to comply with regs.
 