The Power One Aurora family of inverters are roughly as follows:
Air temperature / output
35-40'C: no loss of output (cooling fan gradually increases its speed to cool the internals).
40-45'C: 5-10% loss of output
45-50'C: 15-20% loss of output
50-55'C: 30-40% loss of output
>55'C: major power reduction and risk of shutdown due to overheating
It is also recommended to avoid mounting in direct sunlight as the inverter casing will absorb sun/heat and get hotter than if the inverter is in shade or in a loft/garage/utility room etc.
do you know if that's true for both the indoor and outdoor versions?
useful to know that they start derating 10 degrees lower than the TL series sunny boy inverters, and so aren't as good for loft mounting.